Question Cable testing with a PLC

Hello everyone! I'm Andrea, 27. I've just started working with PLC, but I know all the theory behind it from school.
First thing, I didn't find a "Welcome section" and so I couldn't introduce myself, sorry for that.

But let's begin with my problem. I have to test 30 different channels, just check if all of them are under 1/4 Ohm of resistance. I have to do it with a PLC, most probably a S7-1200. I was wondering if it's possible to directly connect via software two different outputs or an input and an output. When I say "connect" I mean phisically because otherwise the Fluke multimeter can't detect the correct resistance.
Of course, since I'm a beginner if you are open to other ideas, I'm all ears!

Thanks everybody!
  Reply With Quote
Old June 18th, 2017, 02:45 PM   #2
labeledas
Member
Canada

labeledas is offline
 
labeledas's Avatar
 
Join Date: Apr 2010
Location: Peace River Alberta
Posts: 480
what exactly are you trying to measure. give us a description of the system.

Is it the input channel resistance or your plc of some other device, will this be a one time measurement or a continuous monitoring, since you mention 250 Ω I am assuming you are testing analog input card channels.

you also mention connect via software then connect physically. so do you want your plc to control your physical input output connection. its possible but you will require other hardware, relays, multiplexers, etc...

you mention a fluke meter but also mention you have to do it with a PLC I have never seen an actual resistance input module aside from RTD ones and I don't think those will work for what you are attempting.

Last edited by labeledas; June 18th, 2017 at 02:51 PM.
  Reply With Quote
Old June 18th, 2017, 03:23 PM   #3
mikla90
Member
Italy

mikla90 is offline
 
Join Date: Jun 2017
Location: Italy
Posts: 6
Hi! Basically, I have to build a test bench in which I can check automatically if every single channel has a resistance that is less than 250 mΩ.
What I want to do is this: connect all the channels to the Fluke with the PLC in between them and than use it to switch between all the channels, so that the measure is done on a single channel only when the PLC closes the circuit on that channel.
To do so, I have two ideas:

1- if possible (but I don't think) connect all the I/O and then use the PLC just as a relay to directly connect an input to an output

2- connect every channel on one side to a common cable and then put it in an output. Then, connect the other channels to one output each and then "short out" one channel at a time with the common one.

It's quite tricky to explain, but really easy to understand!
  Reply With Quote
Old June 18th, 2017, 05:27 PM   #4
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,160
I think I see what you're trying to achieve. You have 30 "channels" - for the purposes of simplicity, let's just call it 30 "devices" - and each of them, when measured with a multimeter, should read less than 0.25ohms. The Fluke multimeter will perform the test, your task is simply to create a test rig that, having connected your Fluke to it, will connect each device to the Fluke in turn. Then you watch the Fluke as it cycles through and ensure that each reading is correct. Have I got this right?

A few things you'll need to define.
- What type of outputs are you using? Relay outputs? 24VDC triac outputs?
- How does the "cycling through" need to function? Does activating a certain input (say, input 7) cause the test rig to measure a corresponding device (say, the one connected to output 7)? Or does the test rig just cycle through all 30 devices, with a 2 second pause on each?
- Are these devices just a simple load like a resistor? Or something more complex?
  Reply With Quote
Old June 18th, 2017, 05:45 PM   #5
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,299
I think by "channels" the OP means "conductors". As in a 30 conductor cable or wiring harness.

Instead of connecting the meter to each end of each wire, land them all on some sort of assembly that runs the test.

I suppose you could set something up with RTD modules configured for ohms instead of an RTD standard and get a reading from that. 30 channels of RTD modules might be pretty costly but the time saved might make it worthwhile.

It would help to see a picture of the cable assembly or get more details to give better advice.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old June 18th, 2017, 06:01 PM   #6
mikla90
Member
Italy

mikla90 is offline
 
Join Date: Jun 2017
Location: Italy
Posts: 6
OkiePC is almost right. The wires are just wires, there's nothing in between them. It's a rotary joint that transmit power from one end to the other of the same device.
Let me put it this way. Imagine you have to test an extension cord with 30 wires in it, ok? I've to check if every single one of this cables is under 250 mOhms. To do automatically so, I have to use a PLC. For the measure itself, I have a Fluke multimeter and I "only" need a PLC as some sort of multiplexer. My problem is if it's possible to test one channel at a time according to a schedule I made in the PLC and switching between them with the same PLC. Sorry if I'm not clear enough, but it's 1 am here and I'm very tired.
  Reply With Quote
Old June 18th, 2017, 09:12 PM   #7
shawn_75
Member
United States

shawn_75 is offline
 
Join Date: Apr 2010
Location: KY
Posts: 289
Let's assume that both ends of this cable are terminated in some sort of connector with pins 1 thru 30.

Make a connector for one end that shorts pin 1 to pin 2, pin 3 to pin 4, pin 5 to pin 6, etc... now you have 15 wires to test.

Get 2 16 channel relay output modules. On one relay output module, connect the positive side of the Fluke to the common and all the odd number pins to the outputs. On the other relay output module, connect the negative side of the Fluke to the common and all the even number pins to the outputs.

With the Fluke set to read Ohms, have the PLC turn on the first output in both relay modules. This will give you a resistance reading on wires 1 and 2.

There will be resistance added by the shorting plug and the relay modules, so you'll perhaps need to account for that.

Shawn
  Reply With Quote
Old June 18th, 2017, 09:53 PM   #8
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 463
I think your problem is not the PLC sequencing through the 30 lines (that’s easy to setup) but the switch itself.
.25 ohms in not much to work with. At a bare minimum you will need a relay that has bifurcated contacts that are gold plated or maybe mercury wetted contacts ( as much as I hate to see them used anymore) neither of those are available in a PLC output so you will need an interposing relay that will have a constant repeatable resistance across the contacts. Very difficult to find.

I would give some thought to setting up a constant current source switched in to each line and measure the voltage across the line. Still using the bifurcated gold plated contacts.

Set it up to use 30 analog inputs 0-10VCD ( one for each line) then switch in one line at a time give it a 1 sec delay for the current to stabilize and read each input.
Remember any contact will add resistance to the circuit and that will change with every operation of the relay so reading low ohm values through a relay contact would not be reliable a constant current would eliminate the variable resistance of the relay contacts
By using an analog input you could set up a arry in the PLC to store the results for record keeping.
  Reply With Quote
Old June 19th, 2017, 12:00 AM   #9
mikla90
Member
Italy

mikla90 is offline
 
Join Date: Jun 2017
Location: Italy
Posts: 6
The relay solution is the best solution for my purpose. I'll let who's in charge of deciding the components what to use. My curiosity was if it was possible to use only the PLC, but apparently not.
Thanks guys, you're awesome!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Rs logix 5000 varunmahendran91 LIVE PLC Questions And Answers 4 October 6th, 2014 01:26 PM
Read and write data from pc to plc via rs232 cable MANISH VORA LIVE PLC Questions And Answers 4 August 23rd, 2011 01:47 PM
S5 PLC - LAPTOP communicating cable pokajy LIVE PLC Questions And Answers 1 November 12th, 2010 06:34 AM
A link programming cable for Shihlin A-30MR PLC atish_bagchi LIVE PLC Questions And Answers 1 August 5th, 2010 03:00 AM
Medoc(PC) to PLC A1SJ cpu S3 with cable sc09 cannot communication Shehoxs LIVE PLC Questions And Answers 4 June 20th, 2009 05:59 PM


All times are GMT -5. The time now is 08:28 AM.


.