one sensor two inputs
Just a quick newbie question.
Can I connect directly a digital sensor (reflective diffuse) to two independent PLCīs just by splitting up the cable, or is there a specific way to achive this. If it is possible on the other hand.
Old November 14th, 2017, 10:24 AM   #2
janner_10
Supporting Member
United Kingdom
janner_10 is offline
Yes, Just get the sensor to switch a relay and then use that to feed the 2 PLCs
Old November 14th, 2017, 10:36 AM   #3
illibilli
Denmark
yup that will do the trick .
I feel kind of stupid now for not immediately figured that out.
Thanks Kind stranger.
Old November 15th, 2017, 07:11 AM   #4
DwSoFt
Canada
DwSoFt is offline
I'd the inputs are the same type you.could probably do it without the relay as well.
__________________
Dan Wiebe
Automation Manager
Phoenix Energy Services
Old November 15th, 2017, 04:58 PM   #5
ASF
Australia
ASF is offline
Quote:
*Can* but probably *shouldn't*.
There was a thread about this exact topic a little while back - I'll see if I can find it - but the ultimate resolution was that yes, in very specific circumstances and if you take care of certain factors, you can make it work, but it's really not worth the potential headache when a $10 relay will do exactly what you want without any of the potential issues.
Old November 19th, 2017, 09:35 PM   #6
Sergei Troizky
Canada
Sergei Troizky is offline
If a relay has 5 million cycles mechanical life specification, and activates every second, it's theoretical life span is under 2 month of continuous operation.
Also, relay may be not fast enough device for short signals.
I would connect the 0V of both systems, and split the sensor signal to both PLCs, directly or via isolating diodes.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Mapping Inputs in Logix5000 Bering C Sparky LIVE PLC Questions And Answers 11 November 12th, 2014 09:03 AM
Delay OFF on 400 inputs (or more) lauwerstim LIVE PLC Questions And Answers 5 April 19th, 2010 12:45 PM
cpu314 ifm analog inputs tny LIVE PLC Questions And Answers 3 May 18th, 2007 12:10 AM
Use PLC to decide order of inputs roggowb LIVE PLC Questions And Answers 8 February 9th, 2006 10:39 AM
High Density IO TimeFluxCap LIVE PLC Questions And Answers 13 January 22nd, 2005 09:28 AM