random profibus drops

Wondering if anyone has run across an issue like this before.

Machine that's been running for probably 15+ years.

Profibus network physically arranged like so:
servo3-servo2-servo1-hmi-s7300-et200/1-festo1-et200/2-festo2-et200/3

keep getting random bus faults. We eventually figured out that if you turned on the terminator at servo 3 that it would cause a fault. Yesterday the fault came back and I went to the et module at the other end of the network and turned the terminator to the off position, what do you know the fault again went away.

I'm no profibus network guru.

Thanks in advance.
  Reply With Quote
Old November 14th, 2017, 12:56 PM   #2
sigmadelta
Member
Canada

sigmadelta is offline
 
Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 576
Termination should be ON at Servo3 and ET200/3. I would just unilaterally replace the Profibus connector at Servo3.
__________________
Freelance Automation Programmer
  Reply With Quote
Old November 14th, 2017, 01:37 PM   #3
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,509
Termination should be on at both ends of the line. However, you also need to check whether you are using the A and B sides of the connector correctly.

If wrong, turning on the termination will prevent access from one of the sides (can't recall which).
  Reply With Quote
Old November 14th, 2017, 01:40 PM   #4
sigmadelta
Member
Canada

sigmadelta is offline
 
Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 576
The termination switch breaks the "outbound" side of the connector from the device.

At least on Siemens Profibus connectors, the "inbound" Profibus connection point is marked with an arrow towards the connector, and the "outbound" points in the opposite direction.
__________________
Freelance Automation Programmer
  Reply With Quote
Old November 14th, 2017, 02:59 PM   #5
dwoodlock
Member
United States

dwoodlock is offline
 
Join Date: Nov 2012
Location: South Carolina
Posts: 336
Yeah I checked to make sure the cables were entering and exiting on the right side on all connectors, this was my first question when my techs told me what they did to fix the fault.
  Reply With Quote
Old November 15th, 2017, 01:19 AM   #6
ojz0r
Member
Sweden

ojz0r is offline
 
Join Date: Feb 2009
Location: Vaxjo
Posts: 294
I've ran into problems like this with profibus.

Many times it turns out that there is a bad connection in one of the terminations.

In one case it turned out to be a cable that went bad due to the cable moving alot when the machine was running. This fault was found using a profibus analyzer.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Anyoen done Profibus over wireless mattw LIVE PLC Questions And Answers 9 July 12th, 2013 01:55 PM
Siemens S7 Profibus random Node loss Markushaighus LIVE PLC Questions And Answers 2 January 19th, 2013 01:34 PM
Profibus DP in SIVACON MCC installation Ken Roach LIVE PLC Questions And Answers 4 December 5th, 2009 12:55 AM
Profibus network drops Engineer1 LIVE PLC Questions And Answers 3 October 9th, 2009 01:10 AM
S7300 cpu314c-2dp and mp270b using profibus dp tomrobot11 LIVE PLC Questions And Answers 11 April 7th, 2009 06:23 PM


All times are GMT -5. The time now is 11:57 AM.


.