On/Off percentage

Disclaimer: This might be simple - about to have my first grandkid any day now so I'm up late with my daughter and VERY sleepy during the day so my brain is lagging way behind its usual substandard.

Working with a PLC-5. Trying to calc Duty percentage of a pump. Looking for short cycling, not looking for a runtime.

The math is easy: duty% = [Running time] / [cycle time]
Haven't had to do this particular thing before and it caught me that this isn't dead simple, but again, substandard brain.

I haven't tried an OSR yet, I will while I wait for an easier answer, but how else can you time a single bit from true transition to true transition to get the entire cycle time?
  Reply With Quote
Old November 14th, 2017, 03:52 PM   #2
sparkie
Lifetime Supporting Member
United States

sparkie is online now
 
Join Date: Nov 2014
Location: KS
Posts: 636
For the run time use a tl timer while it is running and copy the accumulated value when the timer is deenergized. Perhaps a retentive timer.

For the total time it depends. Is the process cyclical or is it 24/7 Like a water treatment plant.?
  Reply With Quote
Old November 14th, 2017, 04:05 PM   #3
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 688
That would catch the running time, But I need to get the cycle time (On time + Off time)

Its 24x7 as needed, no regularity to it. I also have to have 2 time scales depending on which process it being done. One takes minutes, the other takes
  Reply With Quote
Old November 14th, 2017, 04:15 PM   #4
cwal61
Member
United States

cwal61 is offline
 
Join Date: Jan 2011
Location: NC
Posts: 863
So you want time between true transitions. You are dead on using a OSR.
Rung 1 - OSR Logic
Rung 2 - OSR bit true = MOVE Run Timer.ACC to Storage to capture data
Rung 3 - OSR bit false = Run Timer

This will capture time between OSR Pulse. When OSR transitions to true it will capture data. The next rung will reset timer. The next Scan Cycle Timer starts accumulating next cycle time.


P.S. Congratulations!! May it be healthy and happy.
  Reply With Quote
Old November 14th, 2017, 04:35 PM   #5
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 688
Thanks.
Lets assume this isn't an Enhanced PLC (the ones that can't use the OSR) . How else would you proceed?
  Reply With Quote
Old November 14th, 2017, 05:45 PM   #6
cwal61
Member
United States

cwal61 is offline
 
Join Date: Jan 2011
Location: NC
Posts: 863
Rung 1- XIC Pulse trigger - ONS - OTL (Latch Bit)
Rung 2- XIC Latch Bit - MOVE Cycle Time.ACC to Storage to capture data
Rung 3- XIO Latch Bit run TON Cycle Timer
Rung 4- XIC Latch Bit - OTU Latch Bit

This will keep latch bit true for 2 rungs to Move Data and reset Timer.
  Reply With Quote
Old November 14th, 2017, 05:51 PM   #7
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 688
That should do it. I got the idea. I kept thinking bits didn't resolve until the end of the ladder (like I/O) I know better so thats my problem today.
Man I need a nap !

Thanks for the help.
  Reply With Quote
Old November 14th, 2017, 06:24 PM   #8
sparkie
Lifetime Supporting Member
United States

sparkie is online now
 
Join Date: Nov 2014
Location: KS
Posts: 636
Quote:
Originally Posted by TheWaterboy View Post
That should do it. I got the idea. I kept thinking bits didn't resolve until the end of the ladder (like I/O) I know better so thats my problem today.
Man I need a nap !

Thanks for the help.
Don't be afraid to. Yea, there are times you have to push through, but I've done it. 19 hours into a job I told them I'm going to take a nap. Wake me in an hour. No point to continue if my brain is useless.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
2 motors alternating on/off for 1 second SP3000 LIVE PLC Questions And Answers 2 May 25th, 2017 02:59 PM
Percentage failures for AB 1500 Keithsoccer LIVE PLC Questions And Answers 3 December 31st, 2015 12:42 PM
Turning Output on/off every duty cycle Debangster LIVE PLC Questions And Answers 2 May 14th, 2013 09:12 AM
Omron Zen Output Timed On/Off and Count plewis LIVE PLC Questions And Answers 4 November 18th, 2010 07:03 AM
ON/OFF temperature control markg LIVE PLC Questions And Answers 6 December 13th, 2005 02:36 PM


All times are GMT -5. The time now is 09:33 PM.


.