What is the motor's nameplate rating? 400v/50hz (Wye) / 230v/50hz (Delta)?
If so, wiring it Delta (230v/50hz) you can run 400v/87hz ok. Just be sure the drive can handle the 230v nameplate current, and the rotor is rated for the higher RPM. This is a common 'trick' we've used for years on spindles and such for higher speed applications while still having constant torque.
There's not a real insulation issue, since the voltage to ground and the turn to turn voltage isn't any higher than when wired for the 400v rating...
Exactly and if I may break it down a bit for beginners like myself:
When running a motor in V/Hz or constant torque mode the drive regulates the voltage to increase at the same ratio with the increase in frequency (speed). If a 50Hz motor is wired delta for VAC230
and controlled by a 230VAC drive you have 230/50 = 4.6volta per 1Hz. So for every increase of 1Hz the drive increases the output by 4.6 volts. That allows you to control the motor speed, and maintain constant ratio V/Hz (constant torque), up to 50Hz but beyond that the drive can not maintain the ratio because it is limited by the power supply of 230VAC.
So if you raise the frequency to 60Hz you still have only 230VAC and the consequence of that is loss in torque.
On the other hand if you still wired the motor delta for 230VAC
and controlled it instead with a VFD rated for 400VAC then it will be able to maintain that ratio up to 87Hz which comes out to 400/87 = 4.6V per 1Hz, same as 230/50 and that way you can maintain constant torque up to 87Hz; of course beyond 87Hz you start loosing torque because the drive will not be able to increase the voltage above its supply of 400VAC
Edit: I think I just got your question, you mean to ask what if we follow the same principal and apply it to a motor wired for Y 400VAC? I don't know, that's a good question for the experts to answer. Can we get a 600VAC VFD and run a 400VAC motor, are the motors rated that tightly or is there a range of say 230-800VAC or something like that?
Edit: And now I'm officially hijacking the thread
What if we have 400VAC Y motor and control it with 600VAC up to 33Hz, does that mean we're still running the motor within specs and getting extra torque? Is that something anyone would do or have I lost the plot?