I'm doing the CLX logic for a project using Citect HMI. The guy doing the Citect is having reliability problems with the Citect OPC client to RSLinx.
We initially tried the Citect "RSLinx Driver", but it turned out to have serious limitations as it cannot address members of UDT's within large arrays.
So we changed to using RSLinx as an OPC server and used the generic Citect OPC client. At first it all seemed ok, but we are now seeing very slow updates (> 5 secs) and worse still, we are getting intermittently mis-read data. ie RSLinx will be saying a BOOL = 1 and Citect will say the same BOOL = 0. This is pretty hopeless.
Has anyone out got any advice please?
Does he have the very latest Citect OPC driver? They are updating all the time to suite new gear.
Thank your lucky start it is not BACnet!!! Those speeds are blindingly fast by comparison believe me. I have a system where it takes about 5 minutes to read about 500 BACnet points from a system. The hardware stuff is not too bad (direct from the BMS Controllers) but the stuff from a BACnet software engine is positively painful.
I have had sucess using the Citect driver ABLOGIX to an ethernet
module.
Does not use the RSLinx interface.
Citect V5.21 to ControlLogix 1756-ENET Module.
The key to comms between Scada and ControlLogix is to use Ethernet, as mentioned in another topic.
I am trying to display a variable within a cicode function onto a graphics page. This function queries a SQL database. I can get the value onto a...
272
We are trying to set up a newer generation Omron PLC (NX/NS Series) with Citect / Aveva Plant SCADA using the Ethernet/IP CIP Protocol to read...
341
I am new to Citect SCADA and I am building the graphics for a page that will contain the control of a plant by a Kingfisher RTU. The project I...
248
Hi All, I aim to use Aveva Plant SCADA 2020 to read and write data from/to Omron CJ2M CPU35 PLC using OMFINS protocol. However I have Bad Data...
714
Hey, I'm trying to do the following, I have some experience with Citect but can't seem to figure this out. I/O Tag: BoxPos1_ProdNum (Data Type...
572