PV550 CF card

ThomasGruetter

Lifetime Supporting Member
Join Date
Jan 2010
Location
Florida
Posts
63
Customer reports that they tried to save an application onto a CF card to transfer it to a spare PV550.
The existing PV is 2711-K5A2X. I gave them a CF card (tested) with a demo program on it that we used to test the spare PV.
They powered down their PV and inserted the card then powered up. I was told that the PV automatically loaded the demo program.
Questions:
Is that possible (normal)?
Is the application program lost?
Please comment - I don't have a unit here to test this. I think that it would not
load just any program off the CF card automatically ?
 
The PanelView Standard terminals could not run applications from the Flash card, nor transfer them automatically. You had to access the configuration mode, then perform a Save to Card or a Restore From Card function.

https://rockwellautomation.custhelp.com/app/answers/detail/a_id/44991/page/2


If the "sample application" is running on the terminal, the only logical explanation is that somebody used the Configuration menus to do a Restore From Card operation.

I expect that somebody mis-keyed "Restore From" instead of "Save To".

You can configure a PV+ to run from the expansion card, or to script the loading of specific files when a card is inserted. But those were functions requested while the PV+ was being developed; they didn't exist on the PV Standard.

If a PV Standard has a corrupted application or no application (like after a firmware load) it will go to the Configuration mode and require you to do a download or restore. It will not automatically load from a removable memory flash card.

I'm fairly confident about this answer; I deployed many dozens of PV Standard terminals and I think I would remember such a feature if it existed.
 
Thanks Ken,
Your anser confirms my thoughts - likely the wrong button was pressed.
I really appreciate your feedback and help to many of us AB users.
 

Similar Topics

Hello I need some help, i have a pv550 that every other day give me a 637 fault: communication driver fault, every time I recycled the power the...
Replies
4
Views
2,238
Is there a way to add a stop to the attached program? I want to stop it after the first rinse so the operator would have to push a button for it...
Replies
10
Views
1,211
I'm trying to connect a PV550 (2711-T5A2L) to a 1761-NET-AIC using a 1747-C11 cable (w/RJ45 removed) and the Phoenix connector. Can someone tell...
Replies
8
Views
2,653
We have an old machine that has been mothballed since early 2018 and management are looking at more work for it in 2022. The system runs on an SLC...
Replies
12
Views
2,845
Trying to write a program for a PV550 (2711-T5A16L1, Ser. B, Rev. E, FRN 4.46) to test the touchscreen. I wrote a program with 16 pages and on...
Replies
2
Views
1,684
Back
Top Bottom