Soft starter with forward/reverse?

Karsten

Member
Join Date
Feb 2006
Location
Odense
Posts
158
Hello,

I am looking for a Soft starter with forward/reverse?

Frequency inverters of course have this function but I am looking for a soft starter.
 
The only ones I have seen, use a Forward - Reverse contactor with the soft start
the problem would be with the leakage with the solid state components
it would be phase to phase short.
 
Hello,

I am looking for a Soft starter with forward/reverse?

Frequency inverters of course have this function but I am looking for a soft starter.

I`ve never heard of a reversing soft start.

I`d be interested if it takes less space than the starter and the soft start ;)
 
There are a few out there that can Jog reverse. They pulse the 1/2 waves in the reverse sequence :)

Emotron is one that comes to mind: https://www.emotron.com/products/softstarters/

Slow speed and jog operations
Apart from ramping up and down the speed between zero and rated motor speed, Emotron TSA softstarters offer low speed operation in both forward and reverse without additional hardware. Slow speed or jogging forward or backward can be useful for aligning a load or having the motor running at low speeds for test or service purposes. Examples of applications where such low speed or jog operation is valuable are loading/unloading of centrifuges or mixers, or positioning feeding conveyors.
 
Out of curiosity, I checked the higher end Siemens softstarters that we some times use 3RW44 and 3RW55. And they actually do have this function. They call it "creep speed in both directions of rotation". The lower end soft starters do not have the function.

Well, learned something today. Maybe I can use it in some application.
 
ABB's high-end PSTX soft starters have a "reverse jog" feature; it's advertised as a way to do clog removal on pumps. Allen-Bradley SMC Flex offers 10% and 20% reverse "Slow Speed" as well.

But to actually run full speed in reverse, every soft starter I have seen uses external reversing contactors. Simple, functional, reliable.
 
Hello,

I am looking for a Soft starter with forward/reverse?

Frequency inverters of course have this function but I am looking for a soft starter.


IMHO VFD's [Frequency Inverters]are a much better solution that "old style" soft starters. AND in most cases less cost and MANY suppliers. I wouldn't waste my time on soft starters anymore.
 
Reversing Starter Without Contactors

There are some reversing solid state starters which do not use contactors. They have 4 additional SCRs which, when turned on, reverse 2 of the phases. Of the total of 10 SCRs, only 6 are turned on at a given time. The extra SCRs and the firing circuits for them add significantly to the cost and reversing contactors are generally cheaper, especially for smaller horsepower units.
Here is a diagram of an Eaton Tru-Start 10 SCR reversing starter.

Solid State Reversing.jpg
 
There are some reversing solid state starters which do not use contactors. They have 4 additional SCRs which, when turned on, reverse 2 of the phases. Of the total of 10 SCRs, only 6 are turned on at a given time. The extra SCRs and the firing circuits for them add significantly to the cost and reversing contactors are generally cheaper, especially for smaller horsepower units.
Here is a diagram of an Eaton Tru-Start 10 SCR reversing starter.

Yes, I didn't know there were still some of the offered, or I would have mentioned it. Back a couple decades ago, they were cheaper than VFD's. Not so much anymore I imagine.


chopin said:
Is it not as easy as to use a relays to revers your phases depending on the requested motor direction

This would efinately cost more than a VFD

BITS N BYTES said:
IMHO VFD's [Frequency Inverters]are a much better solution that "old style" soft starters. AND in most cases less cost and MANY suppliers. I wouldn't waste my time on soft starters anymore.

Very true up to about 100hp. BUT, VFD's are not as robust when you have generated power and other issues.
 
Several soft starter mfrs have, or used to have, 5 pole reversing soft starters. But it has fallen out of favor because it will end up costing more than just adding a reversing contactor, and they tended to be less reliable because people tended to try to abuse them, then short the SCRs. I'm not aware of anyone that still makes a fully solid state reversing soft starter. Benshaw and Motortronics both had them and ceased production. That "Eaton" one mentioned above was actually a brand-labeled product from a Canadian company called SAF Drives called the "SS6", which was an offshoot of the old Saftronics. That product is long obsolete. I believe SAF still makes Soft starters, but they no longer make the SS6 with the Reversing option.
 
Yes, I didn't know there were still some of the offered, or I would have mentioned it. Back a couple decades ago, they were cheaper than VFD's. Not so much anymore I imagine.




This would efinately cost more than a VFD



Very true up to about 100hp. BUT, VFD's are not as robust when you have generated power and other issues.


A VFD is a far more complex device. Fewer components and functions should equal superior long-term reliability for a soft start vs. a VFD.
 

Similar Topics

Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
Replies
0
Views
284
We have a 5 Ton Rheem A/C unit at home We only run it in the Summertime, and sometimes in the Fall. It does have a habit of blowing fuses at...
Replies
18
Views
2,377
I have a customer with an ABB PSE170-600-70 Soft starter running a 125HP Bucket Elevator motor (480V). Its been running fine for several months...
Replies
4
Views
3,189
Hello all i know it isn't a plc question but with time i have seen a lot of knowledge here on motors/drive etc.. When braking with a drive, we...
Replies
18
Views
7,649
Hello I'm wondering if it is possible to add a forward/reverse to an already existing soft starter
Replies
5
Views
1,997