Msg instruction, cannot find target PLC

Hello,

confusion on the msg instruction configuration. We cannot find the target PLC-s in the communication path setup; however, we have made sure all the PlC-s are connected using rslinx classic and we can ping their ip address in the command line. Any advice on how to resolve this confusion would be greatly appreciated.

Software: Studio 5000 Logix Designer v31
PLC: Logix 5581E (2), Logix 5571, and EN2T
  Reply With Quote
Old October 3rd, 2018, 04:58 PM   #2
KuulKuum
Member
United States

KuulKuum is offline
 
Join Date: Jun 2006
Location: Texas
Posts: 254
Maybe this Logix 5000 Controllers Messages programming manual will help...

https://literature.rockwellautomatio...m012_-en-p.pdf
  Reply With Quote
Old October 3rd, 2018, 05:42 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,346
If the other controllers are not exchanging Produced/Consumed Tag Data with your ControlLogix, then there is no reason for them to be in the I/O tree.

While having a target device in the I/O tree is convenient, it is not necessary. You can instead compose a CIP path manually.

The User Manual is fairly straightforward explaining how CIP Paths are composed of comma-separated pairs of values for the Port and the Address of each "hop".

You have the new and nifty 5580 series controller, for which the CIP paths can be a little different than the old ones. You don't need the "1, x" to get to the Ethernet module at he beginning of the CIP Path.

Describe which controller holds the MSG instruction, and the IP addresses and slot numbers of each controller, and folks may be able to advise in detail.
  Reply With Quote
Old October 4th, 2018, 01:47 PM   #4
Taelryn
Member
United States

Taelryn is offline
 
Join Date: Aug 2017
Location: Nashua, NH
Posts: 7
I had an issue with this related to a PIO slice I needed to send an explicit message to.

While I could see it in the tree, it would not allow a selection.

I had to give the PIO slice an actual name instead of leaving it blank. Not sure why it mattered in Studio 5000, but it did.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Logix5000 - Unconditional Output behaviour when Faulted lambles LIVE PLC Questions And Answers 12 May 16th, 2017 08:43 PM
rslogix 500 msg instruction don2405 LIVE PLC Questions And Answers 13 September 30th, 2016 12:53 PM
Powerflex 40 start and stop with msg instruction. thiefgold0913 LIVE PLC Questions And Answers 3 March 9th, 2016 02:05 PM
MSG Instruction in an Add-On Instruction -RSLogix 5000 Cleaner LIVE PLC Questions And Answers 4 September 16th, 2013 04:48 PM
SLC5/05 to 5/05 MSG instruction CB_182 LIVE PLC Questions And Answers 3 January 28th, 2009 05:34 PM


All times are GMT -4. The time now is 02:11 PM.


.