Level switches for sewage tanks

Dear,

I am looking for level switches that perform properly in sewage water where there is possibility of flocs and some objects (maybe bags, baby napkins), sewage pumps are located in an airport.
Float switches are not functioning properly specially the one related to low low level because of the presence of some foreign objects in the pit as stated above. Kindly share ideas based on your experience if you have some alternatives.
Thank you
  Reply With Quote
Old February 5th, 2020, 04:35 PM   #2
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 6,049
Floats are usually the old reliable standby. There are different styles, so you might consider alternates.

If float switches are not doing the job I suggest you look at ultrasonic or pressure based switch. And there is always the old reliable bubbler system. https://www.brooksinstrument.com/en/...bubbler-method Just substitute a pressure switch for the pressure transmitter.
  Reply With Quote
Old February 5th, 2020, 05:16 PM   #3
Dryhops
Member
United States

Dryhops is offline
 
Join Date: Jan 2018
Location: California
Posts: 83
You can get fancy and use radar, or ultrasonic sensors that are never actually submerged.

This document is useful as it describes many level measurements options:

https://www.emerson.com/documents/au...s-en-76356.pdf
  Reply With Quote
Old February 5th, 2020, 05:54 PM   #4
kalabdel
Member
Canada

kalabdel is offline
 
Join Date: Feb 2015
Location: Ontario
Posts: 553
Last week I was at a couple location and one has this
in their waster water transfer tank and the other location had this in their treated water holding tank. The pressure switch was for low and low low level and the high and overflow levels had float switches.



I have zero experience with either and read about them to have an overall understanding of the system.
  Reply With Quote
Old February 6th, 2020, 02:25 AM   #5
Caveman
Member
United States

Caveman is offline
 
Caveman's Avatar
 
Join Date: May 2002
Location: Cadiz, Kentucky
Posts: 202
If it is a transfer station, the solids need sucked out once in a while too. Then the floats will work correctly.
__________________
Farmer PLC Tech
  Reply With Quote
Old February 6th, 2020, 07:08 AM   #6
drforsythe
Member
United States

drforsythe is offline
 
Join Date: Aug 2016
Location: Metro Detroit, Michigan
Posts: 91
Ultrasonic and radar sensors work great if you can stay within their working range. There are typically deadbands that need to be avoided at all costs. Because they are electronic, it is good to have them wired and configured in such a manner that will tell your controller if a valid signal is not present (failsafe). Backup or verification sensors are always a good idea in critical processes.
  Reply With Quote
Old February 6th, 2020, 10:33 AM   #7
forqnc
Member
United States

forqnc is offline
 
Join Date: Jul 2009
Location: Elizabeth City
Posts: 80
Why not use a Float switch which travels up and down on a pole, then take some plastic wire mesh and make a tube around it to prevent foreign objects effecting it travel.
  Reply With Quote
Old February 6th, 2020, 06:26 PM   #8
mad4x4
Member
United Kingdom

mad4x4 is offline
 
Join Date: Mar 2009
Location: ST CYrus
Posts: 79
Speak to these guys https://www.pulsar-pm.com/ they handle dirty water all the time sure they will be able to help
  Reply With Quote
Old February 7th, 2020, 03:52 AM   #9
JERA
Member
Denmark

JERA is offline
 
JERA's Avatar
 
Join Date: Feb 2006
Location: Copenhagen
Posts: 304
For sewage water applications I use VEGAPULS WL S 61

https://www.vega.com/en/home_cu/prod...gapuls-wl-s-61
  Reply With Quote
Old February 7th, 2020, 02:30 PM   #10
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 6,049
Some cautions with ultrasonics:
- you can't be too close to a tank wall, or you will get echos off the wall and false readings
- when mounting outdoors wind can cause the echo to drift and cause loss of signal
- if you have foam or floating debris you will get a level reading from them that isn't exactly correct

Bubblers have fallen out of fashion, but they are cheap and reliable.
  Reply With Quote
Old February 7th, 2020, 02:50 PM   #11
mylespetro
Supporting Member
Canada

mylespetro is offline
 
mylespetro's Avatar
 
Join Date: Dec 2015
Location: NS
Posts: 218
Are the floats rod-mounted from the top, or are they mounted on the side of the tank? I've had lots of success using Vega ultrasonic tuning fork switches, but that was in oil, they might not work if something got hung over the top of the fork.
  Reply With Quote
Old February 7th, 2020, 03:24 PM   #12
Oceansoul
Member
United Kingdom

Oceansoul is offline
 
Join Date: Apr 2010
Location: England
Posts: 279
Pulsar (as mentioned above) and very good in waste application's, we use them almost exclusively in our sewerage pump station's (lift station's). We also use the Vega WL S61 radars and they are very good, loop powered instrument with Bluetooth (for easy maintenance). I would recommend the Vega personally.
  Reply With Quote
Old February 7th, 2020, 03:43 PM   #13
lesmar96
Lifetime Supporting Member
United States

lesmar96 is offline
 
Join Date: May 2017
Location: PA
Posts: 408
Quote:
Originally Posted by Tom Jenkins View Post
Some cautions with ultrasonics:
- you can't be too close to a tank wall, or you will get echos off the wall and false readings
- when mounting outdoors wind can cause the echo to drift and cause loss of signal
- if you have foam or floating debris you will get a level reading from them that isn't exactly correct

Bubblers have fallen out of fashion, but they are cheap and reliable.
This is good advice. I have an application personally right now in a lift station that foam seems to be throwing it off. How do you recommend handling a problem like that? Do you use float backup in case something makes the sensor inaccurate?
__________________
Whatever you are, be a good one.
  Reply With Quote
Old February 7th, 2020, 03:48 PM   #14
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,553
Quote:
Originally Posted by lesmar96 View Post
This is good advice. I have an application personally right now in a lift station that foam seems to be throwing it off. How do you recommend handling a problem like that? Do you use float backup in case something makes the sensor inaccurate?
At least one low level float to keep the pumps from running dry.
__________________
You can choose a ready guide in some celestial voice. If you choose not to decide you still have made a choice.
  Reply With Quote
Old February 7th, 2020, 04:00 PM   #15
Oceansoul
Member
United Kingdom

Oceansoul is offline
 
Join Date: Apr 2010
Location: England
Posts: 279
Quote:
Originally Posted by lesmar96 View Post
This is good advice. I have an application personally right now in a lift station that foam seems to be throwing it off. How do you recommend handling a problem like that? Do you use float backup in case something makes the sensor inaccurate?

Radar.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Float Level vs Conductive level Charbel LIVE PLC Questions And Answers 9 January 23rd, 2015 06:52 PM
PID control of level in 2 tanks -Process Question MorphuisOGrady LIVE PLC Questions And Answers 14 April 13th, 2014 03:46 PM
Level Controller Start delay knadeem LIVE PLC Questions And Answers 5 February 15th, 2010 07:58 AM
Lift problem Ladyscarlet99 LIVE PLC Questions And Answers 12 February 16th, 2004 11:39 AM
Counter Question Kunjal LIVE PLC Questions And Answers 3 November 30th, 2002 11:14 AM


All times are GMT -4. The time now is 10:35 PM.


.