Level switches for sewage tanks
Dear,
I am looking for level switches that perform properly in sewage water where there is possibility of flocs and some objects (maybe bags, baby napkins), sewage pumps are located in an airport. Float switches are not functioning properly specially the one related to low low level because of the presence of some foreign objects in the pit as stated above. Kindly share ideas based on your experience if you have some alternatives. Thank you |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
Floats are usually the old reliable standby. There are different styles, so you might consider alternates.
If float switches are not doing the job I suggest you look at ultrasonic or pressure based switch. And there is always the old reliable bubbler system. https://www.brooksinstrument.com/en/...bubbler-method Just substitute a pressure switch for the pressure transmitter. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Jan 2018
Location: California
Posts: 84
|
You can get fancy and use radar, or ultrasonic sensors that are never actually submerged.
This document is useful as it describes many level measurements options: https://www.emerson.com/documents/au...s-en-76356.pdf |
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Feb 2015
Location: Ontario
Posts: 653
|
Last week I was at a couple location and one has this
in their waster water transfer tank and the other location had this in their treated water holding tank. The pressure switch was for low and low low level and the high and overflow levels had float switches. I have zero experience with either and read about them to have an overall understanding of the system. |
![]() |
![]() |
#5 |
Member
|
If it is a transfer station, the solids need sucked out once in a while too. Then the floats will work correctly.
__________________
Farmer PLC Tech |
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Aug 2016
Location: Metro Detroit, Michigan
Posts: 131
|
Ultrasonic and radar sensors work great if you can stay within their working range. There are typically deadbands that need to be avoided at all costs. Because they are electronic, it is good to have them wired and configured in such a manner that will tell your controller if a valid signal is not present (failsafe). Backup or verification sensors are always a good idea in critical processes.
|
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Jul 2009
Location: Elizabeth City
Posts: 93
|
Why not use a Float switch which travels up and down on a pole, then take some plastic wire mesh and make a tube around it to prevent foreign objects effecting it travel.
|
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Mar 2009
Location: ST CYrus
Posts: 98
|
Speak to these guys https://www.pulsar-pm.com/ they handle dirty water all the time sure they will be able to help
|
![]() |
![]() |
#9 |
Member
|
For sewage water applications I use VEGAPULS WL S 61
https://www.vega.com/en/home_cu/prod...gapuls-wl-s-61 |
![]() |
![]() |
#10 |
Lifetime Supporting Member
|
Some cautions with ultrasonics:
- you can't be too close to a tank wall, or you will get echos off the wall and false readings - when mounting outdoors wind can cause the echo to drift and cause loss of signal - if you have foam or floating debris you will get a level reading from them that isn't exactly correct Bubblers have fallen out of fashion, but they are cheap and reliable. |
![]() |
![]() |
#11 |
Supporting Member
|
Are the floats rod-mounted from the top, or are they mounted on the side of the tank? I've had lots of success using Vega ultrasonic tuning fork switches, but that was in oil, they might not work if something got hung over the top of the fork.
|
![]() |
![]() |
#12 |
Member
![]() ![]() Join Date: Apr 2010
Location: England
Posts: 284
|
Pulsar (as mentioned above) and very good in waste application's, we use them almost exclusively in our sewerage pump station's (lift station's). We also use the Vega WL S61 radars and they are very good, loop powered instrument with Bluetooth (for easy maintenance). I would recommend the Vega personally.
|
![]() |
![]() |
#13 | |
Lifetime Supporting Member
![]() ![]() Join Date: May 2017
Location: PA
Posts: 462
|
Quote:
__________________
Whatever you are, be a good one. |
|
![]() |
![]() |
#14 |
Lifetime Supporting Member
|
At least one low level float to keep the pumps from running dry.
__________________
You can choose a ready guide in some celestial voice. If you choose not to decide you still have made a choice. |
![]() |
![]() |
#15 |
Member
![]() ![]() Join Date: Apr 2010
Location: England
Posts: 284
|
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Float Level vs Conductive level | Charbel | LIVE PLC Questions And Answers | 9 | January 23rd, 2015 06:52 PM |
PID control of level in 2 tanks -Process Question | MorphuisOGrady | LIVE PLC Questions And Answers | 14 | April 13th, 2014 03:46 PM |
Level Controller Start delay | knadeem | LIVE PLC Questions And Answers | 5 | February 15th, 2010 07:58 AM |
Lift problem | Ladyscarlet99 | LIVE PLC Questions And Answers | 12 | February 16th, 2004 11:39 AM |
Counter Question | Kunjal | LIVE PLC Questions And Answers | 3 | November 30th, 2002 11:14 AM |