I have a weird problem that I hope is indicative of something simple that someone here can help me with.

I'm using a 24v input, 0-10v output, Vac-45psi pressure transducer. I'm supplying + and - from my 24v power supply to the transducer. I'm taking the signal from the transducer and sending it to the IV1(+) terminal on my Micrologix 1100. The IA COM terminal is getting - from my 24v power supply.

Everything seems to work fine for hours at a time, until randomly the pressure reading will be full vacuum when it should be something else. Applying pressure to the transducer doesn't change anything. I checked the voltage from IV1(+) to my - terminal on the power supply...0V.

What's going on? Anything I should check? Why does cycling the power solve the problem?o_O

Thanks in advance,
Dave

What I've found is when I remove power to the control system and then power up again, the problem goes away. For reference the voltage between IV1(+) and - on the 24v power supply is around 2.4V at atmospheric pressure after powering up again.
 
I am using a raw value of 255 as my atmospheric pressure point.

If the value is >255 then the scale parameters are:
Input Min: 255
Input Max: 1023
Scaled Min: 0.0
Scaled Max: 45.0

If the value is <255 (vacuum) then the scale parameters are:
Input Min: 0
Input Max: 255
Scaled Min: -30.0
Scaled Max: 0.0

What do you mean by data specs?
 
What is the voltage reading at this point
it would help to post your logic also

The voltage is 0.0V when the error is occurring and 2.4V after powering up again (actual pressure is atmospheric in both cases)

I can post my logic but wouldn't you agree that the error is occurring independent of the logic?
 
I have a weird problem that I hope is indicative of something simple that someone here can help me with.

I'm using a 24v input, 0-10v output, Vac-45psi pressure transducer. I'm supplying + and - from my 24v power supply to the transducer. I'm taking the signal from the transducer and sending it to the IV1(+) terminal on my Micrologix 1100. The IA COM terminal is getting - from my 24v power supply.

Everything seems to work fine for hours at a time, until randomly the pressure reading will be full vacuum when it should be something else. Applying pressure to the transducer doesn't change anything. I checked the voltage from IV1(+) to my - terminal on the power supply...0V.

What's going on? Anything I should check? Why does cycling the power solve the problem?o_O

Thanks in advance,
Dave

What I've found is when I remove power to the control system and then power up again, the problem goes away. For reference the voltage between IV1(+) and - on the 24v power supply is around 2.4V at atmospheric pressure after powering up again.

How often does this problem occur? If often, then I would remove the sensor from the system and bench test it with a DMM probing the output terminal. If the output looks abnormal, then the problem is isolated to the sensor or the supply.
 
The voltage is 0.0V when the error is occurring and 2.4V after powering up again (actual pressure is atmospheric in both cases)

I can post my logic but wouldn't you agree that the error is occurring independent of the logic?

Sounds like it. I would still isolate the sensor from the system to bench test it just in case the problem is the analog input channel.
 
I am using a raw value of 255 as my atmospheric pressure point.

If the value is >255 then the scale parameters are:
Input Min: 255
Input Max: 1023
Scaled Min: 0.0
Scaled Max: 45.0

If the value is <255 (vacuum) then the scale parameters are:
Input Min: 0
Input Max: 255
Scaled Min: -30.0
Scaled Max: 0.0

Aside from your transmitter problem, why not just scale the input once?

Input Min: 0
Input Max: 1023
Scaled Min: -30
Scaled Max: 45

And are you sure its "PSI" and not "inHG"?

Just curious.
 
Aside from your transmitter problem, why not just scale the input once?

Input Min: 0
Input Max: 1023
Scaled Min: -30
Scaled Max: 45

And are you sure its "PSI" and not "inHG"?

Just curious.

Scaling once for above atmospheric (psig) and once for below atmospheric (inHg).
 
I suspect an intermittently bad connection.

If you have 0 volts (when there is not a vacuum) across the analog input (+) to (-), then either

1) the power supply is bad or not making connection to the transmitter, or

2) the transmitter is not producing the correct output, or

3) there is an open circuit preventing the transmitter's voltage from reaching the AI or from powering the transmitter (same as 1).

I'd look for #3 first.
 

Similar Topics

Good morning everybody, I hope you are very well. I share with you the information of the PLC LOGO! Siemens and expansions that we have...
Replies
4
Views
1,081
Has any used a ballistic pressure transducer with a PLC? I am not sure if it will capture the event that I need to use as a control. The device...
Replies
2
Views
1,077
I am updating controls on a leak tester, from a SLC 5/02 to Compact Logix. The SLC used a DDV instruction to help scale a differential pressure...
Replies
17
Views
4,408
A little background info I work at a underground coal mine. We have a Dust tank capable of holding 135 tons of rock dust on the surface. We use...
Replies
10
Views
1,621
Hi Guys, Is a typical transducer programmed to output its signal in intervals? Say every 10 seconds it would generate a signal via 4-20mA loop...
Replies
3
Views
1,642
Back
Top Bottom