Please look at the attached RSLogix5000 screen capture.
I am checking for IO card fault in a remote ControlLogix chassis. I have another 8 similar rungs above rung 8 for checking the status of the remaining IO cards.
Will this logic give me an IO card fault if a card is pulled out of it's slot or if a card is missing, i.e. will tag XA_0139B be set?
Thanks.

iocardfault.jpg
 
Yes, that looks like a good way to check the FaultCode objects for all of the I/O modules in your system. You can use it for modules in the local chassis as well as on ControlNet or EtherNet/IP networks.

I'd condition the logic to run occasionally instead of every scan. That FBC takes up a little scan time and you don't need to run it any faster than necessary to check on the I/O modules.
 
Ken, I used this logic for checking IO card fault at one site. Didn't test the logic at that time. Later, the customer pulled out a couple of modules but says that he didn't get an IO card fault alarm. I need to go to site and check it.
My doubt is whether the fault code changes from 0 to some other value if a module is pulled out from its slot. Is a fault code generated if a module is not present in its slot?
 

Similar Topics

An issue occurred at an organization here in whereby the ControlNet card developed a fault. Card Details: Catalog/Series; 1756-CN2RXT B Part No...
Replies
0
Views
422
Dear experts I have a system of Rockwell contrllogix in which I have used about 16 analog module..1756-if16 card.but during commissioning there is...
Replies
2
Views
1,934
Are any of you guys out there aware of a consolidated list of I/O cards that can be replaced online? We just replaced a 1756-IF16 card while the...
Replies
2
Views
1,461
I have a project to upgrade an old 1756-L55 to a newer CPU. The customer wants added functionality and the old CPU is limited to RSL v16. The...
Replies
5
Views
2,114
1) I am currently trying to integrate a Prosoft MVI56E-MCM Module into a 1756-L61 CONTROLLOGIX5561 that is a redundant system (CPU is redundant...
Replies
13
Views
3,355
Back
Top Bottom