How can I connect a Hall Effect Flow Sensor Pulse output to PLC?
kunalv
Sep 2019
India
28
Hey guys,
I am building a small prototype for a Coolant Dispensing System and need to measure the flow rate of water & chemical in the pipe in order to control the opening of valves downstream.
Since I am building a small pilot system, I can't really spend too much money and hence I intend to use those cheap Hall Effect Flow Sensors available online. Accuracy isn't important right now, but repeatability is!
So my question, how do I connect the Pulse Output of the Flow Sensor to the PLC?
It is for 5VDC.
You would normally use a signal conditioner 5VDC/24VDC to get the signal into the PLC.
A less expensive solution is to use a simple relay with 5VDC coil voltage.
You also need a power supply that outputs 5VDC.
It is for 5VDC.
Thanks for the suggestion JesperMP.
So the Pulse output of the sensor goes to the 5VDC relay, output of which is fed to the PLC right? How do I configure the PLC to read this?
I'm sorry if this sounds stupid, as I honestly am not into Electronics. If you can draw a simple sketch, I'd be indebted to you! Thanks.
As I see from the datasheet you have attached the sensor has supply voltage range 5 - 24V so you can directly connect it to a PLC input.
You cant use relays it this application.
It is for 5VDC.
That's the problem, you know, since these are commercially available low-cost sensors (probably made in China), there is no authentic technical literature available other than what you find online.
I have been advised to use an Optocoupler with the sensor so as to scale the output from 5V to 24VDC and use a PLC with a high-speed counter card. Can someone verify this please?
I have cheap Chinese flowmeters like you have and they worked with 24V but you have to be careful.
You can use an optocoupler, a mosfet or a transistor if you don't want to risk supply the flowmeter with 24VDC. Then you measure the frequency of the pulses to calculate the flow in L/min.
You can also use 5V input card a Jesper suggest.
What kind of PLC do you have?
It's possible that you will need a pull-up resistor as well.
I haven't purchased a PLC yet mainly because I'm not sure which one to get for this application.
Could you tell me what is the need for the pull-up resistor? Is it to convert a 5V signal to 24V for the PLC? Doesn't the Optocoupler do just that?
I have not used that particular unit but have used many others, as it say the unit will work from 5v to 24v so will interface with many PLC's. If you used a Mitsubishi FX range PLC the first 5 inputs are also high speed inputs up to I think 5khz so should be ok. See attached pdf file on how to use the high speed inputs on this PLC.
Note: only X0 used in this application and you must use the counter specifically tied to the input i.e. C235 > these are high speed counters and you do not need to reference X0-X5 as these are automatically assigned to the counters.
I had used Schneider's Zelio SR3 smart relay but it should work with any PLC that has high speed input. Didn't use optocouplers or any other electonics besides pull-transistor.
Check the following article to understand more about flowmeters and pull-up resistors.
https://www.flowmeters.co.uk/flow-meter-output-selecting-optimum-output-flowmeter/
87
99
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
335
What has been your experience with year over year price increases on your Tech-connect service contracts? Is it up to the distributor? 30% seems...
287
Hello, friends, I am trying to upgrade a system that uses an Onrom incremental encoder (E6B2-CWZ6C) connected to a Danfoss VFD (FC360), but now...
271
