Boiler Sequencer ( Lead / Lag )

Join Date
Mar 2016
Location
Chicago, Il
Posts
5
Hi Everyone,

Question regarding Boiler Controls , if anyone would like to chime in. I work for a Boiler OEM where we manufacturer our own Boilers we use siemens and honeywell burner management systems. Now occasionally we will provide a package of 2 or more boilers. If so we provide the customer with duplex boiler sequencer panel, primary boiler would call on secondary if the primary load draw is above a certain percent. Now the 2 boilers that we provide are sized the same so we can generate the same firing rate using header pressure in our PID loop in we output the Firing Rate via a 4-20mA connection to each boiler. We cycle the standby on as necessary based of the primary boilers load demand. One particular customer only wants one of our units but wants sequenced control with an existing boiler that he has on site. the problem is that our boiler is 200 BHP and the existing is 150 BHP. My question is can we proceed in a similar fashion that we do and send both boilers the same firing rate, or would I have to essentially ramp up the standby primary boiler to match the " btu output " of the primary?
 
In cases like that we usually rely on simply using different pressure setpoints and max. working pressures.

For example.

Boiler 1 works on a SP of 10 BAR, with max working pressure at 12 BAR, hysteresis 1 BAR.
Boiler 2 works on a SP of 8 BAR, with max working pressure at 10 BAR, hysteresis 1 BAR.

This way the stand by boiler will start when ever pressure drops below your SP. I have over exaggerated the setpoints, but you get what I mean. This way there is no need for any communication between the boilers or an additional controller.

If you want to go with your solution, I don't see how it would not work. Perhaps if you are determining demand and setting boiler load according to that. But I doubt that is the case.
 
Since the goal is constant pressure in the header does it really matter how you approach the problem. If it were me I would use the 200 BHP boiler as the lead and keep the 150 BHP as a hot standby. the point at which you ramp up the standby boiler is dependent on how fast the load changes.
Ultimately it is up to the customer.
 

Similar Topics

Hello, I have problem i'm working on boiler plc, but i get to the problem that i can't solve myself. I have problem with material gate. I need to...
Replies
2
Views
348
HI All : We have a boiler that can produce up to 75000 lb/hour, this boiler has two CompactLogix Plcs from Allen Bradley , one is used for burner...
Replies
10
Views
3,893
hi everyone im using OPERATOR PANEL SPOT PLUS 150 35W 24VDC AUTOMATA ID42003 (as hmi system) and automata optispark controller to control and...
Replies
8
Views
2,410
All, My client is looking to have me calculate the boiler feed water differential pressure in kPa to and actual flowrate in m3/hr. Once the...
Replies
2
Views
1,512
Good day Gents, Does atmospheric pressure have an influence of a boiler steam pressure.
Replies
31
Views
8,537
Back
Top Bottom