Profibus Communication 555-1106 with S7-224
debest
Feb 2006
Portland, OR
I'm working on a project for a Drinking Water Plant which has a single Simatic 555-1106 PLC for automation.
A small control panel (with an Siemens S7-224 CPU and an EM227 Profibus DP module) will be added to automate some valves that are part of a proprietary system.
The Owner would like to pass timer setpoints to/from the 555-1106 and the S7-224 using Profibus communication.
The 555-1106 has a Profibus DP port on it. I've used this port in other plants (several years ago) to connect with remote I/O bases and with VFD's. I'm not sure if I'm allowed to use it to talk with other PLC's. Can I use Profibus DP for this with the 555-1106 acting as the Master? Or do I need to use Profibus FMS?
Thanks!
Hello debest;
The EM227 is a Profibus-DP slave module; all you need to do ic configure the in/out data table (the addresses you want to contain the exchange data with the 555 CPU) with ComProfibus:
http://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&lang=en&siteid=cseus&aktprim=0&startNode=4000024&nodeID0=10805153&basisview=4000003&viewLevel=6&wttree=cs&foldersopen0=-238-237-186-185-184-243-&jumpto=243
Then export the binairy file from ComProfibus and Merge it in the 555-1106 program.
Basically that is all you have to do. If you have trouble with the details, come back and see us.
Hope this helps,
Daniel Chartier
Dear All, I have a KUKA Palletizer machines having Iconics Genesis SCADA installed on its PC. It remained closed for about 7 to 8 years. We are...
959
Good morning, I am looking to establish a communication between one Profibus master and one Profibus slave. I downloaded the Profibus Master...
58
14,470
We have older Festo electrical servodrives : CMMP-AS-C5-11A-P3 and CMMS-AS-C4-3A with profibus interface cards for control by a Siemens plc. The...
1,247
Hello Everyone! I am looking for a solution for making successful Profibus Communication between ABB 800XA & HOneywell HC90. I had gone through...
2,090
Hello guys, I have problems with the Porfibus communication to my regulator Siemens Sipart DR 21and my PLC rockwell 1756-L161. So, for the...
2,099