AB to Toshiba on RIO

plcman777

Member
Join Date
Oct 2004
Location
Wa.
Posts
25
I have an RIO network of block IO modules and one Toshiba G3 Drive.

My network works fine, all block IO modules are doing thier thing.

My question is for the Toshiba.
Toshiba RIO addresses go from 1 to 255 and AB go from 0 to 3.

So if my Toshiba is Rack 2 do I address it 2,3,127 or 128 or none of the above?

I tried Toshiba tech support already, they don't know either.

Thanks
 
When you say that the "A-B RIO addresses" go from 0 to 3, you are probably talking about a 1747-SN RIO scanner.

If you set the Toshiba as Rack 02, then it will show up in the I/O image for the slot of the 1747-SN.

Where "x" is the Slot number:

I:x.0 through I:x.7 Rack 00
I:x.8 through I:x.15 Rack 01
I:x.16 through I:x.23 Rack 02
I:x.24 through I:x.31 Rack 03

O:x.0 through O:x.7 Rack 00
O:x.8 through O:x.15 Rack 01
O:x.16 through O:x.23 Rack 02
O:x.24 through O:x.31 Rack 03
 
Last edited:

Similar Topics

I lost a main board today that holds all parameters for this very old drive. I got the drive back to where it can be started and ran, but I lost...
Replies
0
Views
1,713
Hi, I have two Toshiba G3 Tosvert-130, one of them I can see monitoring mode, I can control with the LCD display, recently I changed the presets...
Replies
1
Views
338
I inherited a system with the Micrologix 1500 talking to 8 VFDs using Modbus RTU protocol. One of the VFDs was replaced with a Toshiba VF AS1...
Replies
1
Views
1,184
Another software thread! We have a Toshiba EX100 that's just been working away quietly in a panel for 20 years, never causing a problem to...
Replies
1
Views
1,197
Hi, Any body had success to change parameters in between a Toshiba Inverter VF-S11 using a Red Lion any series (mine is K304), and MODBUS RTU...
Replies
1
Views
1,141
Back
Top Bottom