DirectSoft 6 - Modbus
ThomasGruetter
Jan 2010
Florida
63
PLC model D0-06DD2-D: I uploaded the program from a defective unit and installed it in a new PLC.
Com port 2 is used for modbus communication to 2 drives. The communication to the drives on the new PLC does not seem to work. The port was setup properly under PLC/Setup/Setup Sec. Comm. Port... with same parameters as on the old unit.
Is there something I missed ? I also up/downloaded v-memory data.
Note this is my first time using DirectSoft.
Tried that and switched PLC's several times to see if I missed something.
The port setup is okay and don't think that port is defective out of the box.
So I missed something else?
What was the problem with the PLC you replaced? Was the drive communications working with the original PLC?
The old PLC has welded output relays.
The code is using SP116 and a 1 second time bit (SP4) as conditions to send the drive command (speed).
The condition is NOT SP116 and SP4 then modbus command.
The SP116 seems to be in on state and the signal command never gets excecuted?
As I don't understand what SP116 is I might just remove it and see if it works.
The SP116 bit is true when the port is busy. There is also a SP117 bit which is defined as "Port error". You should check that.
I'm not fond of your logic. SP4 is on for 500 mS and off for 500 mS. There is a better example in the DL06 manual on page 4-28. You need to take steps to make sure you only process one MRX or MWX per program scan.
That is the part I don't understand. What is SP116? It is used 4 times and the condition seems always off - therefore command is not sent. The second drive is using the time bit on condition. Forgot to attach earlier. I guess trying to avoid collision of commands?
SP116 and SP117 are special relays in the DirectLOGIC CPUs that monitor the PLC’s communications. SP116 is on when Port 2 is communicating with another device
I found using Stage logic best for sequential communication commands. One command per stage. In each stage just wait for the busy bit (SP116 in this example) to be off then trigger the MWX/MRX command then JMP to the next stage. The last stage JMPs to the first.
Hey im using the directsoft 5 software for a DL06 PLC. Im pulling signals in from the modbus port 2 from a slave third party device. Im having...
2,335
I am not a Automation Direct programmer. I have done a lot of RS500 I have the DS5 software and I am able to look at the program. I am reaching...
1,175
Hello, I have a couple of problems with the directsoft 6 software. I couldn't find a previous answer, and uninstalling and reinstall hasn't...
1,475
Hello all, We have an old AutomationDirect DL405 (CPU 440) PLC, and we've been using DirectSOFT 5.3. Since we are NOT upgrading this PLC for a few...
2,261
Hey everyone, Working on a system with a Koyo DL06 processor and it's my first experience with them. I have DirectSoft 6 and we got the program...
2,330