jwyatt8171
Member
Hey Guys,
I have several thermoforming ovens I am working on. These ovens have 24 heating zones. Each zone may be from 2 heaters in series, to 20 heaters in series parallel configuration. These are what we call cal rods, resistive heaters. 480V system where one zone has 2 SSRs, and L2 doesnt go through an SSR, but is connected (I can upload examples of the wiring if needed.
i have been tasked with setting up diagnostics through the HMI. I am having trouble getting started on this. Space is limited, and I would rather not install new SSRs.
My first through is to use CT(current transformer) connected to analog inputs to the PLC. Can a CT output be connected to a 0-20ma input? I have found some compact CTs that are rated 0-100A with 26ma max output. the highest fuse rating on a zone at the moment is 40amps.
My theory is to have a base amps the zone pulls, and if its out of tolerance we can show a warning for the operator to act on.
Thanks for any input.
Jerry
I have several thermoforming ovens I am working on. These ovens have 24 heating zones. Each zone may be from 2 heaters in series, to 20 heaters in series parallel configuration. These are what we call cal rods, resistive heaters. 480V system where one zone has 2 SSRs, and L2 doesnt go through an SSR, but is connected (I can upload examples of the wiring if needed.
i have been tasked with setting up diagnostics through the HMI. I am having trouble getting started on this. Space is limited, and I would rather not install new SSRs.
My first through is to use CT(current transformer) connected to analog inputs to the PLC. Can a CT output be connected to a 0-20ma input? I have found some compact CTs that are rated 0-100A with 26ma max output. the highest fuse rating on a zone at the moment is 40amps.
My theory is to have a base amps the zone pulls, and if its out of tolerance we can show a warning for the operator to act on.
Thanks for any input.
Jerry