Hey guys,
Although I've poured through this forum for help in the past this is my first post.
I am looking at replacing obsolete Baumer IVO Parallel encoders. It is a PLC 5 platform currently. I have installed a logix chassis for a previous upgrade and have a 1756-RIO card in that chassis as an adapter to get data back and forth between logix and PLC5. I'm going to be using an 842E-M encoder from AB for this upgrade. My plan is to RIO the encoder data from Logix to the PLC 5. Currently the encoder data is brought into the PLC in gray code via a 16 bit flex io input card. My plan is to set up more RIO racks and just change the current PLC logic to accept the data from my ethernet encoder rather than the flex IO input.
I have two questions.
1)My encoder data on the logix side is stored in a DINT. PLC5 works in 16bit words (INTs). But my encoders are all scaled where they don't exceed a maximum 16 bit value of 65536. Am I able to move this data to the PLC5 without any further manipulation?
2)With a 1756-RIO card in Adapter mode, am I able to move across data or am I limited to strictly inputs and outputs on the PLC5 side? I realize its ALL data technically on the logix side, but I'm under the impression I have no choice here but to land my data FROM Logix into the input data table on the PLC side. Am I correct here? So that being said I'll have to move my raw encoder position on the logix side into a DINT I would have set up to be my RIO rack and that will land in the corresponding input table in PLC5? Is there a way to move data into an integer file for example?
Thanks in advance for the assist on this.
Old August 4th, 2022, 03:12 PM   #2
Ugsomania
Canada
Just a little update I'm currently benchtesting this...
I have my encoder position coming into a dint. I'm scaled to 0-65536 and have successfully moved this into an INT output tag that is set up to RIO to the PLC5. I have data coming into my PLC5 input word I:010.
On the logix side I have my encoder counting properly up to 65536 and then rolling over. However on the plc5 side once I get to 32767 the next value goes to -32767.
Is there a way to use the entire positive range of the 16 bit input word in the plc5?
Old August 4th, 2022, 03:18 PM   #3
drbitboy
United States
drbitboy is offline
drbitboy's Avatar
Yes.
Actually the next value is -32768, not -32767.
I assume you are MOVing the INT tag to the DINT tag, after that, AND the DINT with 65535 (0000ffffh), and values of -32768 to -1 in the INT will will be 32768 to to 65535 in the DINT.
__________________
_
Brian T. Carcich
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
iii) Measurement is hard.
iv) I solemnly swear that I am up to no good
Old August 4th, 2022, 03:39 PM   #4
drbitboy
United States
drbitboy is offline
drbitboy's Avatar
Oh wait, I think I misunderstood the query: the problem may be whether the PLC-5 has unsigned INTs or 32-bit DINTs.
PLC-5 does have floats, so you could MOVe the INT value (e.g. I3.5 or N7:0) to an element of a float file (e.g. F8:0), and then add 65536 to it if the INT value is negative:
Code:
MOV N7:0 F8:0
XIC N7:0/15    ADD F8:0 65536.0 F8:0
Alternate, probably clearer:
Code:
MOV N7:0 F8:0
LES N7:0 0    ADD F8:0 65536.0 F8:0
Floats have 23 bits of mantissa, so there will be no loss of data.
__________________
_
Brian T. Carcich
Old August 4th, 2022, 04:51 PM   #5
Lare
Finland
Lare is offline
Code:
MOV N7:0 F8:0
Code:
MOV N7:0 F8:0
Thinking that four compares or rungs should also work for setpoint comparing but code isn't so clear.
If encoder setpoint is positive number (setpoint is less than 32768) and encoder value is positive -> bigger or equal compare
If encoder setpoint is positive number (setpoint is less than 32768) and encoder value is negative -> less compare
If encoder setpoint is negative number (bigger than 32767) and encoder value is positive -> less compare
If encoder setpoint is negative number (bigger than 32767) and encoder value is negative -> bigger or equal compare
Old August 4th, 2022, 05:54 PM   #6
drbitboy
United States
drbitboy is offline
drbitboy's Avatar
Quote:
Originally Posted by Lare View Post
Thinking that four compares or rungs should also work for setpoint comparing but code isn't so clear. ...
If all one wants is the direction and offset from current encoder value to the setpoint (or vice versa), then it's even simpler than that.
But this raises a question: why does it matter to OP whether the encoder is either in the range [0:65536) or in the range [-32768:+32768)? Both ranges are continuous, except at the rollover, if this is a rotary encoder.
__________________
_
Brian T. Carcich
Old August 5th, 2022, 09:00 AM   #7
Ugsomania
Canada
Thanks for the responses. After digging a little further I've found that for the application rolling over to the negative value has no consequence. I'm fairly new to the design and commissioning side of this game. Learning everyday.
Thanks again!!
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
How to calculate absolute encoder position? g.mccormick LIVE PLC Questions And Answers 20 May 22nd, 2018 05:51 AM
SLC 505 ethernet code sample for pwerflex drives. mmiles LIVE PLC Questions And Answers 4 December 5th, 2009 10:13 AM
Gray code encoder on SLC 5/05 Joe Smalling LIVE PLC Questions And Answers 4 June 5th, 2006 12:38 PM
Gray encoder pauly LIVE PLC Questions And Answers 10 May 11th, 2006 04:38 AM
AB Encoder Code Steve_D LIVE PLC Questions And Answers 4 August 19th, 2002 09:52 AM