GridConnect DeviceNet Detective vs V2 vs NetAlert! DN-MTR
Years ago. DevicNet Guru (Ken Roach) helped me out on a job and told me to get troubleshooting tools. So I carry a Devicnet Detective, a netmeter, and every different devicnet connector you can think of. I charge a premium to get these tools out of the service van. They are always in there.
Long back story I will try to make short. As I remember the events its need more the a few years ago. I did a system PLC, 2 ABB robots and a conveyor on DNet. It was running for years. I got called that the robots where faulting. Both ABB where reporting that they could only be in controlled by 1 master. The conveyor had a photoeye on it that was powered off the DNet bus. The sensor cable was worn thru by the conveyor belt lacing. When the metal lacing shorted out the DC bus the conveyor I/O module 100-DNY would take the network down. The ABB robots tried to reboot the slave units and saw that they where already part of a scsnlist and faulted out on a multiple master fault.
I used both the Detective and Netmeter to see the DC bus go low and high. I don't carry a scope with me.
Ken Roach feel free to correct my diagnosis or terminology where I screwed it up. It was been. Many years since back then.
I get called out about once or twice a year on DeviceNet issues. About every 3 yo 5 years yo start up a new MCC with DeviceNet.
I found one of these Netalert! meters locally, trying to determine if it works without having access to a Device Network at the moment.
When I turn it on with no connection, it reads about +2.2 volts on either position 9 and 11, and -0.2 volts :( on the 7 position. I was expecting to see 0 volts...
If anyone has one handy sometime, could you flip in on and see what you get on 7, 9 and 11 open circuited?
Hello All, I am trying to connect a XPORT-EIP-MB (adaptor which converts Modbus RTU/ASCII to a EtherNet/IP) to a ControlLogix5561 PLC and to read...
1,557
Dear all, I am trying to send out a message from Allen Bradley ControlLogix Controller (Logix5555) via the EtherNet/IP Module 1756-ENET to...
5,868
Hi, I am looking to migrate some of our Electronic Overloads off of a Troublesome Devicenet Segment. Is there any documentation confirming the...
88
We've run into an old system that we are upgrading which is still running Steeplechase with Citect using Devicenet to Wago. I had some experience...
146
Sigh, DeviceNet noob... I have a 1756-L55, with a DeviceNet module, and 10 PF700 all commanded with DeviceNet. One of the PF700's blew up...
133