stuck on a simple bit issue...brain fog as per usual
Skidood
Oct 2016
Ontario
215
Hi Group
See the photo.
Will this work? I previously had the "contactor outputs used as inputs" tied directly to the IO DIG OUT coils, and what happened was, Valve 2 did not activate when Contactor 1 was ON.
Then I added the extra bits as shown but I think I'm still breaking a rule and haven't really changed anything.
i can't figure out how to do this any differently....help!
BTW..It might be evident to you all, but what I want is Valves 1 and 2 both energized when Pump 1 is ON, and only Valve 2 energized when Pump 2 is ON. Pump 1 and Pump 2 never run at the same time, its either one or the other.
Thank you so much...
[re-formatted:]
  1. Valves 1 and 2 both energized when Pump 1 is ON, and
  2. only Valve 2 energized when Pump 2 is ON.
  3. Pump 1 and Pump 2 never run at the same time, its either one or the other.
So stated another way:
  • Valve 1 is on when Pump 1 is on
    • Valve 1 is unaffected by Pump 2's On/Off state
  • Valve 2 is on when
    • EITHER Pump 1 is on
    • OR Pump 2 is on.
[N.B. Fixed the "Canonical" comments; thank you kamenges!]
Code:
     Pump1On   Valve1
-------] [------( )---      ### Canonical [C := A]
     Pump1On    Valve2
---+---] [---+----( )---    ### Canonical [D := A or B]
   | Pump2On |
N'cest pas?
Btw, I would still code summat for a violation of case 3 e.g. an alarm that summat (sensor?) is amiss.
Originally posted by drbitboy:
Pump1On Valve1
-------] [------( )--- ### Canonical [if A then C]
Pump1On Valve2
---+---] [---+----( )--- ### Canonical [if A or B then D]
| Pump2On |
I am going to get a little semantic here but, since words really do matter, I'll risk it.
Either a very important precondition was not stated in the diagram above or the canonical descriptions are incomplete. In that description form it should be:
if A then C
else NOT C
This is something that drives plc users that come from text based languages a little nutty sometimes. The standard coil implementation in all plcs that I know of contains an inferred "else NOT" function.
Another way of thinking of this is
"C = A" in the first case and
"C = (A OR B)" in the second.
Keith
if A then C
else NOT C
Keith
d'Oh, thank you, yes, I mis-posted, my mistake, this is much better., I will fix it.
Did I at least get the ladder right? ;)
Hello. I am very new into PLC and am still learning basic logic and the commands using the LogixPro 500 software. My teacher assigned us a...
4,460
Hi, I am using M221 reading from 3 different sensors (modbus rs485) sharing same bus (daisy chain). I am currently using READ_VAR (in total...
83
I'm using one TON (called SystemTimer) throughout a program that I change the .PRE given different conditions. I'm porting an IDEC ladder over to...
314
We have a keg check weigher that that lost a fight to a forklift. The scale was previously a Systec IT3000, which was the only PROFIBUS slave...
671
really strange issue. The panelview(2711p-T10C22D9P) will try to load an application and get stuck on "Starting Alarms". If I reboot the...
1,433