I have a project at a lab on a university that has (qty) 15, 20 amp breakers in a panel feeding all of the receptacles/outlets for that lab. The breaker panel feeds multiple labs, so I cannot turn off the main. I need to take control and shunt trip or turn off these 15 breakers in the event a condition is met (gas detected or a hand station pushed).


Does anyone know a way to take control of 15 (qty), 20 amp breakers and turn them off?
 
Do you have the space in the panel for 15 individual shunt trip breakers? Or is it possible to put one large shunt trip breaker that supplies a subpanel that houses the 15 normal circuit breakers?
 
Do you have the space in the panel for 15 individual shunt trip breakers? Or is it possible to put one large shunt trip breaker that supplies a subpanel that houses the 15 normal circuit breakers?


There is no space for shunt trip breakers unless the same size as a standard 20 amp breaker. I may have to add a subpanel assuming the conductors are long enough and then shunt them all with a main in the sub panel.
 
Gas, eh ?
Since gas is involved, is it a concern due to the risk of explosion or the risk of poisoning ?

I doubt that achieving the sufficient risk reduction can be done by tripping circuit breakers.
Do a Risk assessment.
Chose safety category according to risk assessment.
Connect contactors and safety relays according to the chosen safety category.
If the risks are sufficiently high, you may need dual redundant contactors.
If there is a risk of explosion, you must consider EX.

Over here there are Class C standards for specific applications, which MUST be followed if they exist for a specific application. I am guessing that something like that exist for what you are working with.
 
Hi all!
I have a project at a lab on a university that has (qty) 15, 20 amp breakers in a panel feeding all of the receptacles/outlets for that lab. The breaker panel feeds multiple labs, so I cannot turn off the main. I need to take control and shunt trip or turn off these 15 breakers in the event a condition is met (gas detected or a hand station pushed).


Does anyone know a way to take control of 15 (qty), 20 amp breakers and turn them off?

What make and model of breaker are they ? Are they MCB or MCCB ?
 
may I suggest that you post the question on an electrical web site.

I am a member of mike.holt.com and they will be more than happy to answer your question. you failed to mention what state, lab classification, and possible gasses.

I am a member of the website and have no association with them.

james
 
Gas, eh ?
Since gas is involved, is it a concern due to the risk of explosion or the risk of poisoning ?

I doubt that achieving the sufficient risk reduction can be done by tripping circuit breakers.
Do a Risk assessment.
Chose safety category according to risk assessment.
Connect contactors and safety relays according to the chosen safety category.
If the risks are sufficiently high, you may need dual redundant contactors.
If there is a risk of explosion, you must consider EX.

Over here there are Class C standards for specific applications, which MUST be followed if they exist for a specific application. I am guessing that something like that exist for what you are working with.


Yes, these are petroleum engineering doctorates using methane for experimental purpose. We sniff the perimeter and experiment area for methane and shut down the lab electrics and methane sources via solenoid, there is constant exhaust in the lab that will pull the gas outdoors and hopefully not into a smoking area!
 
This is a safety issue.
I think that in the US, you can be personally liable.
So I think that you should be very certain that you know what you do, since you can get yourself into some serious trouble.

If this was a machine, you should start with a risk assessment. It is not trivial.
I dont know the safety standards for laboratories, it is possible they are more strict than for machines (!).
At the very least, you should try to find someone with know-how about the subject who knows the general direction you should go.
 
I'm unsure of the breaker type. A standard Square D panel if that helps. I will have to perform another walk through.

No such thing as a standard Square D panel i'm afraid.

Ignoring all the safety concerns for the time being and dealing with it solely on the electrical front, without the MCB or MCCB model and make there isn't much more anybody can add.
 
there is constant exhaust in the lab that will pull the gas outdoors and hopefully not into a smoking area!
Don't these experiments need to be done in a ventilated hood where there is no chance for leaking methane (natural gas) to escape? That's what the lab hoods are there for.

A circuit breaker that trips/breaks (or makes) is an arcing/sparking ignition source that has to be in a 'safe' area where there is no exposure to methane.
 
No disrespect intended, but the fact you have come here asking questions proves your are outside of you're area of competence.

It's been many years since I was a practicing electrician, but this doesn't sound like the sort of job you want any old 'sparks bodging some shunt trip and hope for the best.

Sounds like a case for someone experienced in this field.
 

Similar Topics

Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
Replies
10
Views
482
Hi fellas, Hoping someone can help me get started with this. I'm a little out of my comfort zone trying to set up communication with a ProFace...
Replies
0
Views
827
I have a text display "Word Lamp" that I need to change the background color of if any one of 3 (sometimes 4) PLC bits are ON, and on top of all...
Replies
3
Views
4,114
Afternoon all, I'm working on setting up a large excel recipe table for porting updates through the Linx Gateway RTD/DDE function into my recipe...
Replies
2
Views
93
I'm a Manufacturing Engineer with limited PLC experience and I am doing some research for our Controls Department. Does anyone have experience...
Replies
4
Views
173
Back
Top Bottom