Safey issue with motors & VFDs

rdrast is correct in his assessment of the problem with the instantaneous and time delayed safety outputs.

What is being described here is referred to as a Category 1 stop as per NFPA 79 (section 9.2.2, 2002 edition). This is a controlled stop, where power is being used to control the stopping action, then having power removed after the safe stopping of the system.

I also agree with rdrast that I never put equipment in the field that does not have an isolation contactor between the drive and the motor. The only way that I would not do that is if the drive manufacturer can supply documentation indicating the drive will operate at a level of safety without the isolation contactor that satisfies your risk assessment. (Do you have one of those?)

Of course, with a 10 second wind down, I do not see a way around a solenoid locking safety switch (power to open, prefferably). The time delay output on the safety circuit is good, but a zero speed detector is better. This will be more reliable over the long haul.

Using a brake motor for this application is not the best idea from my expereince. I typically try to use brake motors for "holding" loads, not stopping them. Using them to stop the load will significantly reduce the longevity of the motor (also braking time will vary, see note above). If you are anticipating this happening only ocassionally, then it probably isn't a problem. If this is something that is going to happen more frequently, then you may need to consider the longevity of the system. Additionally, in some applications you want the motor to spin freely with the power off (like spindle applications, so that you can tram stuff). With a brake motor, this is more difficult.
 

Similar Topics

Hi all smart and knowledgeable people.I have a hmi connected to 2 Plcs via ethernet.These 2 Plcs connected to control 2 systems in one machine...
Replies
2
Views
92
Hello everybody, I have Kinetix 5500 (2198-H040-ERS). I'm having issue with this drive. (I believe it's the drive/Kinetix and need confirmation)...
Replies
0
Views
60
Hi Everyone, I am facing an issue while installing the STUDIO 5000 in my windows 10 PC. During installation I am getting an error that " Error...
Replies
4
Views
181
Hello all. I am trying to communicate to an ASi gateway from my CpLX (L16ER). I am able to ping the gateway and it replies. I configured the...
Replies
5
Views
160
Hello All! I am writing today because I cannot figure this out for the life of me. Another site I am affiliated with keeps having their slc 5/03s...
Replies
29
Views
473
Back
Top Bottom