SLC 500 4-20 mA output and pneumatic valve
BobVuTo
Jun 2010
New Orleans
I send the value of 32767 the output which suppose to open the valve 100%, but it didn't. The old controller (Bailey) could open/close the valve with its 4-20 mA signal. What could be wrong here? Thanks for your help.
Bob
Bob
There are a lot of possibiities! First, have you checked at the actuator to make sure you actually have 4-20 mA there? You should also check the voltage across the valve operator with the wires terminated at 4 and at 20 mA. Have you checked the wiring diagrams on both to make sure you don't have a ground loop? Are you sure that the Bailey and the PLC output are both self powered or both loop powered? Have you tried moving the valve using a simulator at the panel to make sure the wiring wasn't pulled loose? Have you verified that the PLC is actually giving you 20 mA?
what catalog number output module are you using? ...
for many of them, 31208 is the magic number which will get you 20 mA (not 32767) ...
for 4 mA try 6242 ...
give us more information and we can probably offer more detailed help ...
A customer asked if I could change an output address in a SLC 500 that he thinks is bad. I've not worked with that PLC before, so I asked him to...
2,604
Experts, I have an issue with an Allen Bradley SLC-500 Output Board. The PLC is going through it ladder logic correctly and the Output terminal...
4,071
Hello. We are having issues with a SLC 500 rack. Cause of the problem: We had a 1746-OB32 Ser A card giving a nice smoke effect from it. On...
2,512
Is there a simple way to monitor if there is a major fault on the plc. Looking at my systems there is no output to our scada system for a major...
2,504
Hi friens i need your help.... Anyone know slc 500 k card could be used to control an actuator output of 4-20 .... I await your thoughtful...
1,435