1734-IR2 and IT2I
Snyd1
Jun 2018
there
225
Anyone that has these thermocouple or RTD cards in use answer a question I have.
Reading the manual they show low scaling endpoint at freezing 0c (32F). My question: does that mean they will not register temperatures below freezing?
You're looking at the table for custom input scaling. That only applies if your application doesn't use temperature inputs. For the usable temperature ranges of each TC and RTD type, go back two pages to the Supported Sensor Types tables.
Thanks completely over looked that. What exactly is the benefit of using one of the specialty cards over a regular analog input and SCP instructions to scale the signal?
The biggest benefit is eliminating RTD or TC transmitters. One of my recent projects had over 450 RTD sensors and head mounted transmitters weren't an option. Using TTs and 8 channel current inputs would have doubled or tripled the size of the remote I/O panels.
There are some negatives to consider: The 1734-IR2 modules have a high backplane current draw, limiting them to three on the adapter and five per expansion power supply. With communication limits, there's a practical limit of 18 modules per Ethernet node. Each adapter and module require a CIP connection to the processor. We used almost half of the 512 connections available in an L72 processor.
An ordinary analog card is built for a different voltage or signal range, with A/D converters of different precision and range, and different protective circuitry.
The 1734-IT2I has a sensitivity of 2.5 microvolts per count, while the 1734-IE2V has a sensitivity of 320 microvolts/count.
And ordinary analog modules don't have the onboard non-linear scaling lookup tables that are standard for thermocouples (in the case of the -IT2).
Another drawback to using sensitive input circuits is that they're generally delicate. Connect 24V DC to a thermocouple input module and you will damage it.
But the fact that I can connect a Cold-Junction Compensator to the module (another specific feature of the Thermocouple module) and get an accurate value of temperature in tenths of a degree is a big benefit to simplification of my programming and HMI.
Hello! I have RTD sensor with 4 wire and shield ( 2 red wire + 2 white wire + Shield) and I want to connect to 1734-IR2 module. But in the manual...
1,473
Hi Guys I have few questions regarding a setup of a RTD input module 1734-IR2, the module is in a Point I/O rack with a Ethernet Adapter...
6,228
To get values from an Allen-Bradley 1734-VHSC24 module, which is a high-speed counter module for CompactLogix PLCs, you typically use software...
45
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
97
27
1,215
