FM200 panel vs fire alarm panel

Charbel

Member
Join Date
Jan 2012
Location
Beirut
Posts
307
Dear,

I have a room which is being served by FM200 panel and fire alarm panel is used for monitoring,

in case of smoke detection, FM200 panel will turn off the ventilation (fans off, close motorized dampers, shutdown louver and turn off split units) and fire alarm panel is only monitoring FM200 panel,

is this the common practice or usually fire alarm panel will control the ventilation and dampers?

thank you!

charbel
 
That’s going to depend on local regulations. In North America the fire alarm panel has to comply with strict standards. I don’t know if this restricts it from doing any sort of control however I spent 25 years in the fire service and I never saw a fire alarm panel that did anything other than monitor and notify (no control). My guess is that it can’t, it can only be a system monitor.
 
New York, U.S. based systems integrator.

Our experience has been that there is the fire alarm system, then there is the "fire panel", which is where firefighters go to control all HVAC related equipment; dampers, fans, etc.

When we integrate building controls, fire panel controls must have final control over all HVAC control elements. Because fire panel must be able to control these devices,regardless of status of building controls, PLC-based or otherwise, consideration must be given during integration. Typically, hard-wired control signals must be switchable at fire panel between building control and fire panel control.

Different authorities have different rules.
 

Similar Topics

Is there anyone who can help me regarding this HMI is missing the choices when I make a new Device in TIA. Only 7" Display above are the choices...
Replies
3
Views
80
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
204
We are considering dropping our UL membership because most of our customers do not care if we are a 508A shop. However, there may be times when a...
Replies
8
Views
396
Hello, I need to create an automatic transfer panel that connects to the generator when the mains power is cut. I can draw up to 60kW and draw up...
Replies
0
Views
84
Am asking if we can upgrade sd ram and cf card of panel view plus ab by a normal sd ram and cf card but Allen Bradley to save cost because in ab...
Replies
9
Views
281
Back
Top Bottom