PV 300 and micrologix 1500

zaskew

Member
Join Date
Oct 2018
Location
florida
Posts
5
Purchased a new PV 300 because old screen keypad not working but still getting communication signal. Do I used panel builder 32 software to get them communicating? Can I use a memory card and upload from PV 300?
 
PB32 will get you going, and so should the memory card.

You might have to press and hold in the "COMMS" button (top-center of the ML1500) to switch it from COMM0 to DCOMM or vice-versa.

https://www.youtube.com/watch?v=97UMwBIgvzw
https://www.youtube.com/watch?v=gIhZpIBsu60

And we have a ML1500 here that we have to stop the RSLinx driver and restart it to re-establish comms each time we do a download. You might have to do the same thing.
 