Can't upgrade firmware for CompactLogix L32E

Hi everybody

I hope you can help me.
Im trying to upgrade the firmware , but dont get sucess. This is the log I get from ControlFlash:

Quote:
9/11/17 16:18:23 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/11/17 16:18:52 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/11/17 16:18:54 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/18/17 12:21:59 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/18/17 12:22:03 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/18/17 12:22:04 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/18/17 12:22:14 [FAILURE] Device Identity: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/18/17 18:16:09 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/18/17 18:16:12 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/18/17 18:16:13 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/18/17 18:16:18 [FAILURE] Device Identity: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/25/17 12:00:43 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/25/17 12:00:48 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/25/17 12:00:48 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/25/17 12:08:33 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/25/17 12:08:35 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/25/17 12:08:35 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/25/17 16:32:40 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/25/17 16:32:43 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/25/17 16:32:44 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/25/17 17:14:36 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/25/17 17:14:45 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/25/17 17:14:45 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/25/17 17:14:49 [FAILURE] Device Identity: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/25/17 17:14:59 [FAILURE] Device Identity: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/26/17 12:09:37 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/26/17 12:09:39 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/26/17 12:09:40 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/26/17 12:10:06 [FAILURE] Device Identity: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/26/17 12:10:29 [FAILURE] Device Identity: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/26/17 15:32:26 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/26/17 15:32:29 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/26/17 15:32:29 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/26/17 15:32:33 [FAILURE] Device Identity: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/26/17 15:33:52 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/26/17 15:34:11 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/26/17 15:34:11 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/26/17 15:34:14 [FAILURE] Device Identity: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/26/17 15:44:13 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/26/17 15:44:18 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/26/17 15:44:18 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/26/17 15:45:06 [SUCCESS] Device Identity: Path = RSLinx API!AB_ETHIP-1 16 13 49 57 50 46 49 54 56 46 49 46 49 48 51 0 1 0, Instance = 1,
VID=0x0001, PT=0x000E, PC=0x004D, Maj Rev=01, Min Rev=15, SN=0x403D01BE

09/26/17 15:45:27 [SUCCESS] Validate:
VID=0x0001, PT=0x000E, PC=0x004D, Maj Rev=01, Min Rev=15

09/26/17 15:45:27 [SUCCESS] Authorization: Bypass cookie used.
Key: PN-133555

09/26/17 15:45:52 [SUCCESS] Device Identity: Path = RSLinx API!AB_ETHIP-1 16 13 49 57 50 46 49 54 56 46 49 46 49 48 51 0 1 0, Instance = 1,
VID=0x0001, PT=0x000E, PC=0x004D, Maj Rev=01, Min Rev=15, SN=0x403D01BE

09/26/17 15:45:56 [SUCCESS] Validate:
VID=0x0001, PT=0x000E, PC=0x004D, Maj Rev=01, Min Rev=15

09/26/17 15:45:56 [SUCCESS] Authorization: Bypass cookie used.
Key: PN-133555

09/26/17 15:46:03 [SUCCESS] Load Script: C:\Program Files (x86)\ControlFLASH\0001\000E\004D\PN-133555.nvs

09/26/17 15:46:03 [SUCCESS] Program: Catalog Number = 1769-L32E/A LOGIX5332E, Serial Number = 403D01BE, Num Updates = 3, Size = 6243840 byte(s).

09/26/17 15:46:09 [SUCCESS] Update: Instance = 3, Size = 2836168 byte(s), Chunk Size = 128 byte(s), Major Rev = 20, Minor Rev = 11

09/26/17 15:52:27 [FAILURE] Reset: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/26/17 15:52:35 [FAILURE] Reset:

09/26/17 15:53:54 [FAILURE] Update: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/28/17 17:12:59 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.

09/28/17 17:13:04 [SUCCESS] Load Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/28/17 17:13:04 [SUCCESS] Initialize Driver: C:\Program Files (x86)\Common Files\Rockwell\AB_ASA.DLL

09/28/17 17:14:12 [SUCCESS] Device Identity: Path = RSLinx API!AB_ETHIP-1 16 13 49 57 50 46 49 54 56 46 49 46 49 48 51 0 1 0, Instance = 1,
VID=0x0001, PT=0x000E, PC=0x004D, Maj Rev=20, Min Rev=11, SN=0x403D01BE

09/28/17 17:14:16 [SUCCESS] Validate:
VID=0x0001, PT=0x000E, PC=0x004D, Maj Rev=20, Min Rev=11

09/28/17 17:14:16 [SUCCESS] Authorization: Bypass cookie used.
Key: PN-133555

09/28/17 17:14:22 [SUCCESS] Load Script: C:\Program Files (x86)\ControlFLASH\0001\000E\004D\PN-133555.nvs

09/28/17 17:14:22 [SUCCESS] Program: Catalog Number = 1769-L32E/A LOGIX5332E, Serial Number = 403D01BE, Num Updates = 3, Size = 6243840 byte(s).

09/28/17 17:14:24 [SUCCESS] Update: Instance = 3, Size = 2836168 byte(s), Chunk Size = 256 byte(s), Major Rev = 20, Minor Rev = 11

09/28/17 17:18:55 [FAILURE] Reset: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/28/17 17:19:02 [FAILURE] Reset:

09/28/17 17:20:21 [FAILURE] Update: Error #11003: Unconnected Send timed out waiting for a response.
GS=0x01, ES=0x0204

09/28/17 17:34:22 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.
The first package is sent. The PC "lose communication" after the power up operation

Thanks in advance

Last edited by mabauti; September 28th, 2017 at 05:51 PM.
  Reply With Quote
Old September 28th, 2017, 07:13 PM   #2
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,606
Opening observations from the log file...

You are attempting a flash using the Ethernet port.

The 1769-L32E processor is flashed to firmware revision 20.11 - 1st part, then first reboot fails.

What is most likely happening is that ControlFlash is attempting a "Polling for powerup", which automatically reboots the controller, and the Ethernet port's IP address configuration is being reset. This often happens when a Static IP address has not been assigned and BOOTP is still active.

Can you verify whether the Ethernet port's configuration is Static or not? Have you or are you disabling BOOTP/DHCP? Do you have to keep reconfiguring the port settings after this issue?

Browse to the controller in RSLinx Classic and right-click on it and open the module properties. Check whether the Ethernet port is set for manual configuration. If not then set it for manual and reboot the controller and check it is retaining its IP address configuration. Double-check that manual setting is still applied and then attempt another flash.

Note: For the flash, I would advise that you make sure you are connecting directly to the controller's Ethernet port and not via a switch, etc. Also, when flashing, have just the controller, the power supply and end cap fitted properly on the CompactBus.

Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Old September 29th, 2017, 06:38 AM   #3
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,606
P.s. I forgot to mention that you should also disable any wireless LAN connections on your workstation.

Here is a good guide to flashing the firmware on the CompactLogix controllers...

65540 - CompactLogix Controllers: Flashing firmware via EtherNet through ControlFlash
Access Level: Everyone

Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Old October 2nd, 2017, 03:00 PM   #4
mabauti
Member
Andorra

mabauti is offline
 
Join Date: Sep 2017
Location: Bahamas
Posts: 9
thanks Geospark

I can comunicate with rs232.I can not comunicate with ethernet.
I did what you told me, this is what I get (atteched image)
Attached Images
File Type: jpg comms.jpg (27.5 KB, 46 views)
  Reply With Quote
Old October 2nd, 2017, 03:38 PM   #5
tarik1978
Member
Morocco

tarik1978 is offline
 
Join Date: Mar 2010
Location: casablanca
Posts: 510
Did you set the network adress of your laptop to a fixed adress Ex: 192.168.1.100?
Also as George said, disable the wirless.
  Reply With Quote
Old October 3rd, 2017, 03:08 PM   #6
mabauti
Member
Andorra

mabauti is offline
 
Join Date: Sep 2017
Location: Bahamas
Posts: 9
Done!

I did both: I had forgotten to set a static IP and assign a stable IP to my PC

Thanks a lot Geospark

Thanks a lot tarik1978
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
L32E firmware upgrade 13 to 19 issues robw53 LIVE PLC Questions And Answers 12 January 22nd, 2013 05:51 AM
Firmware Upgrade of PV Plus to Ver 6 chavak LIVE PLC Questions And Answers 5 December 18th, 2011 04:57 AM
panelview550 firmware upgrade problem wolf3000 LIVE PLC Questions And Answers 1 January 26th, 2011 02:16 PM
FM 357-2 firmware upgrade vlad.colesnic LIVE PLC Questions And Answers 0 November 16th, 2008 09:19 AM
1747-SDN Firmware Upgrade? 504bloke LIVE PLC Questions And Answers 5 August 4th, 2005 04:48 AM


All times are GMT -5. The time now is 01:42 PM.


.