Automation Direct C-more Touchscreen HMI button turning on/off on its own.
unsaint32
Oct 2012
minneapolis
365
Our Automation Direct HMI's one push button is activating on and off on its own without anyone touching the HMI button. I power cycled the HMI and the problem went away. It happened twice in the last three weeks.
I verified that it was the HMI issue by going online to Controllogix and seeing the tag for the HMI button changing between 0 and 1 continually. No other tag triggers taht tag.
C-more V2.78 was used to program the HMI. The button's a simple PB configuration. The HMI is ea7 t15c touch screen.
Has anyone had a similar problem?
Good Morning,
Short of swapping screens and see if problem follows. Is this a new install? you could try moving the button to a different part of the screen. I have not seen this issue before in C-More I have seen it with Proface.
Tom
I have had this problem with an EA7 15".
It ended up being a bad screen. The touch cells were intermittently activating even with no pressure.
I had a touchscreen that messed up badly after the concrete floor in a shop was cut to put in a pit for a new press. The concrete dust contained sharp shards that penetrated the touch screen & shorted out many contact points when the operators pressed on them.
Check & see if any construction like this has been around, or even heavy metal grinding in the area.
Hello all. I've been working with Do-More designer for the past two years. I used to work with AB before then, but since the company I work with...
2,518
I'm having serious trouble trying to get the recipe function to work. I'm using an EA9-15" with a Productivity 2000 plc. My "recipe" consists of...
3,841
Good Evening , How easy is it to setup and communicate with a AB MicroLogix with a C-More EA-3 HMI ( Serial ) ? Thanks for your help and...
1,535
Hey all, I'm working on a project where there are some existing remote sites that are using Automation Direct DL05 PLCs. They're very simple...
3,277
I have a compactlogix L32E. I am connecting about 20 Automation Direct C-More touch screens to it. The current PLC Protocol I am using to...
5,758