Sensor Voltage Problems

noob saibot

Member
Join Date
Aug 2005
Location
Vancouver, BC
Posts
16
Hi Guys and Gals,

I have an AST4600 Pressure sensor connected to an Allen-Bradley Micrologix 1200 PLC via the 1762-IF4 module.

The problem is that the sensor reads the correct output voltage when disconnected from the PLC, but gets "pinned down" in voltage when connected.

Lets say I have 5800psi on the sensor, it will read 4.127V with the sensor disconnected which is just fine. When I connect it I read 3.083V at that same pressure, which is wrong. When I reduce the pressure on the sensor, it remains at 3.083V until I get to 3800psi in which it will read correctly and give me the correct voltage that I can translate to the correct pressure. So its basically Translating any pressure above 3800psi to 3.083V when the sensor is connected to the input module.

What is going on here? I had the same problem when trying to use small voltage dividers (potentiometer and resistor to adjust voltage) to simulate a pressure sensor on the 1762-IF4 input, however it worked with a benchtop power supply using the voltage. I have called AST and they can't seem to see any reason for it.

The specs of the sensor are:

10-28VDC Excitation
1-5V output (0-7500psi)
output impedance <100ohms, nominal
current consumption <10mA
Bandwidth (-3dB): DC to 1kHz
Output Noise <2mV RMS
Output load 5k Ohms Min.

Thanks in advance....
 
It may be an incorrectly configuration/connection at analog input module. If the module configured for 4-20 mA input it may bring your voltage down when you connect your transmitter to it. Check you analog module configuration and connection. Sometime it is require some jumpers to be moved also.
 
As val_99 says. Heres a picture. ( note factory default is current)

DipSwitches.jpg
 
100 ohm output impedance of the transmitter trying to drive 250 ohms at the input, an equivalent circuit of 71.4 ohms. No wonder the voltage signal caved in . . .

Dan
 

Similar Topics

Hello everyone! I just opened a new LRTB200C laser sensor that i got from keyence. I have hooked a 4 wire quick disconnect cable to it with Brown...
Replies
1
Views
1,431
HI All, Can anyone please recommend a few reliable pressure sensors, which can provide output in terms of voltages? My plc has built in analogue...
Replies
13
Views
4,620
I have an omron E3F2-R2Z1 photo sensor connected to a 125v source and attempting to drive a delay relay. When the sensor switches it outputs...
Replies
22
Views
5,314
Hi everyone, I am working with micro850, a proximity sensor (FOTEK, PL-05P) and a 3DOF serial arm robot. I use MC_MoveRelative to control the...
Replies
1
Views
31
Maybe a stretch to call this a PLC question, but it does connect to a PLC input. I have two German switches: Sick WL9LG-3P2232 And a...
Replies
0
Views
103
Back
Top Bottom