Siemens S7 FB41 cont c
sean mark
Jul 2006
hull
Hello
I am trying to understand the operation and all the parameters required for setting up the FB 41 block, I have read the Siemens manuals but I am still a bit confused. My process is pretty simple, I have a room temperature transmitter (4-20mA) that controls the operation of a cold glycol diverting valve with 0-10vdc control and position signals. I have to control the room temperature at between -5degC to +10 degC (operator selects temperature setpoint via HMI). Any help would be helpful.
Cheers
Sean
sean mark said:
Hello
Cheers
Sean
Hi Sean,
In the attachement you can see a test with PID project. There is an emulated heater process in it, so that you don't have to connect anything to see the PID work !!.
U can use the Siemens PID Tool to optimize your process:
If u use this, make sure that you can go online, choose ONLINE in this tool and open your DB41 (the online PID DATA). Then you can optimize grafically.
If I remember correctly, if you require cooling instead of heating then set a negative figure in the proportional gain.
hi there
I was trying the project attached by the combo
Problem is am able to open the DB41 in the "PID Control" but cannot get online.
Iam simulating the project in the PLCSIM.
Ok
manmeetvirdi said:
hi there
I does work in simulation, I'm sure. When you open the 'PID Control' you need to check the online first, then browse the online DB41
hello, I'm new in automatics, and i'm working on a speed control project for a hydraulic turbine. i'm using FB41 pid bloc, but the LMN give me 0...
2,241
Hi everybody, I am searching for some advices regarding PID controller with FB41. My program is designed for online blending with 2-3 components...
3,438
Hi If I enable INT_Hold when QLMN_HLM or QLMN_LLM are on would this freeze the integrator and prevent the windup of the integrator? As I see it...
4,209
Hello all, I am an electrical engineering student working on a senior design project with an industry sponsor. We are automating a burst test...
26
13,884
Hi all. I have problem starting up a mixing plant. There is 4 PID loops in the control system. PID for: Flow Working range 0-30000 kg/h by...
2,269