Old February 13th, 2020, 06:55 AM   #16
Bit_Bucket_07
United States
Bit_Bucket_07 is offline
Bit_Bucket_07's Avatar
Quote:
Originally Posted by thingstodo View Post
OK - I learned something!
I don't expect that the new soft starts fixed the OTHER big issue ... 30% - 50% of rated torque on start?
I've been working with soft start drives since their inception, and I can't recall ever encountering such an absurdly small starting torque limit.
__________________
Old February 13th, 2020, 07:27 AM   #17
Gene Bond
United States
Gene Bond is offline
Soft Start means just that!
You normally set the initial current/torque/voltage (depending on mode or model), then the max current/torque/voltage, and it ramps it up.
IF the starter is sized properly for the application, the load will start, as the max amps can be set as high as Locked Rotor Amps...
Old February 13th, 2020, 11:52 AM   #18
jraef
United States
jraef is offline
jraef's Avatar
Fix? Thatís the entire PURPOSE of a soft starter...
Old February 13th, 2020, 06:17 PM   #19
thingstodo
Canada
thingstodo is offline
Quote:
Limiting the starting current limits the starting torque, doesn't it?
This is a snippet from a Rockwell white paper. I can't find anything that shows more starting torque that what is listed here.
https://literature.rockwellautomatio...p007_-en-p.pdf
@jraef and @Gene Bond - we use these on centrifugal fans and impeller pumps, since they have very low starting torque required.
I know that, in the past, some mines used a fairly complicated setup to start conveyors with MULTIPLE 250 HP motors (to get enough starting torque) and then essentially shut off all but one when the conveyor was up to speed. Is that still done?
I would think that a VFD to start up a constant torque load like a conveyor would make more sense. You can use a bypass contactor to run at full speed after it's been accelerated ... ?
Old February 13th, 2020, 06:34 PM   #20
jraef
United States
jraef is offline
jraef's Avatar
Just for posterity, since this was written years ago and is dropping off of the radar, I suggest that if the subject of how and when to use various starting methods is of interest, download and save this somewhat more comprehensive White Paper. The only way I could find the link now was because I already knew the exact name, otherwise I couldn't find it on Rockwell's site.
It's called "Starting High Inertia Loads: A Comparison of Starting Options"
Old February 13th, 2020, 07:33 PM   #21
Gene Bond
United States
We still use a lot of them on Crushers, Shredders and Grinders of >100HP.
As far as the big, long conveyors, there are still some out there on soft starters, but VFD's do most of it now, where one is the master and the others are torque followers, to share the load. The biggest issue with multiple motors on 1 load is that the motors really need to bematched if they are fed from the same power source (rather than individually controlled). Otherwise, 1 motor may wind up with the majority of the load.
I don't know if anyone still does it, but a few were using bypass contactors on VFD's if a fan was running at 100%, and then transition back if the demand lowered. It was not as good IMO as the energy saving setting on modern drives, which can reduce the voltage when the load is lighter than 100%.
That's a good paper jref. I somewhere have a similar one written by one of the guys at Saftronics from a good while back (1980?). It did not mention VFD's for obvious reasons back then (nobody made an economical and reliable VFD back then)
Old February 13th, 2020, 08:57 PM   #22
thingstodo
Canada
Thanks for the link. I'll add it to my library of reference material!
Old February 14th, 2020, 07:41 PM   #23
Mike Lamond
United States
Mike Lamond is offline
Long before that white paper, other engineers devised mechanical means to start those high inertia loads: https://www.youtube.com/watch?v=fNuI6keQXYA
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Star Delta starter vs soft starter ASF LIVE PLC Questions And Answers 10 May 28th, 2019 02:58 AM
AB SMC Flex soft starter srv LIVE PLC Questions And Answers 17 December 19th, 2017 12:30 PM
Can use Soft starter for Construction hoist? mindtool LIVE PLC Questions And Answers 5 June 4th, 2012 11:45 AM
VFD as soft starter nightex LIVE PLC Questions And Answers 16 April 24th, 2012 03:45 AM
To The Soft Starter Experts BobB LIVE PLC Questions And Answers 2 November 25th, 2004 10:12 PM