modbus hmi modbus tcp reads from a wago 750

ganutenator

Lifetime Supporting Member
Join Date
May 2002
Location
kansas
Posts
1,440
Probably something simple, but my project hmi (schneider mounts in a button hole hmi) doesn't seem to be able to read or write to my wago plc.

The plc and hmi project was developed in So Machine and I translated the so machine into codesys for the wago 750 (tough job, I know, right). So I expected the hmi to at least be able to read or write to something.
 
What addresses are you trying to write to? Holding Register Word 0 in the PLC = 12288 in the HMI

thanks!
That worked.
why the offset?
More importantly, If I want to read %MX0.15? Would that be %MW12288.15?

I assume the offset may have something to do w/ registers allocated for I/O?
 
It comes from this table

15frdlh.png



Your syntax for bool is correct
 
I was tasked w/ evaluating the schneider m251 w/ so machine vs the wago 750-852? w/ codesys.
Wago totally won via dif. from to ports on the port forwarding (aka multiple machines at one site), 0-15 bool vs scheider's 0-7 bool thingy.
 

Similar Topics

I have a Red Lion G09 scanning 8 Invertek P2 VFDs via modbus RTU - I've setup necessary comms and tags and all works well. I have a 'Settings'...
Replies
3
Views
1,872
disclaimer- 1,no one in their right mind would pick this configuration but I want to try and get it working. 2, my MB knowledge is sketchy at...
Replies
5
Views
1,139
I am trying to get a Mitsubishi GT2715 HMI to read and write from a Eurotherm 3508 controller using 4 Wire RS485 Mobus RTU communications. The...
Replies
3
Views
1,305
Well, I'm working with this ABB plc project, and It's been a learning experience coming from Allen Bradley. The project can't be changed to an AB...
Replies
1
Views
1,172
Hi everyone, I'm hoping someone has some experience in this because I'm at wits end ready to tear my hair out lol. I have a SP5000 Series Proface...
Replies
2
Views
1,950
Back
Top Bottom