Flex IO communications fault

I would like to ask a question about remote IO faults. I have a small project using PLC5 with a 1794 Analog Module. The analog module is the only module on this Rack. The field devices on the module are LVDT's power by an external 24vdc source with common to ground. Should the analog card be powered by the same 24vdc source as the LVDT's? The 1794-ASB could power the analog reading the publication. I would like to power the analog module from the external supply but I did not know if when the external power supply is powered down to change out a either LVDT if it would fault the ASB with an Adapter Fault of a Local Fault and/or if either would effect operation of other equipment being controlled by the PLC5. Also if a fault, would it clear when power is restored on the Analog Module or could it be cleared by the reset on the ASB?

Any help would be appreciated.

  Reply With Quote
Old December 17th, 2006, 08:24 AM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,854
Sounds good like it is...

It is usually best to keep your I/O power supply separate from the ASB power supply. It should be okay to replace a faulty LVDT without turning off power to the analog card adapter module. In addition, you can remove power from the device side of the analog module without faulting it, and disconnect signal wires if necessary. Your analog readings will go to the minimum values, and the PLC will respond how it has been programmed when those values change.

If you power down the 1794-ASB and the PLC5 is still up and running, you will get a rack fault for that rack in the "S" status file in the PLC5. This is a minor fault which will not halt the processor. The PLC program will continue to run and the other I/O will not be affected.

The output image bits in the PLC5 for the affected modules will either be reset or hold their last states, depending on how you set the dip switches for the 1794-ASB.

The PLC can be configured to continually try to restore communication by setting the dipswitch for "allow processor restart". If that dipswitch is not set, the technician must initiate a reset of the rack to restore communication. When communication is restored, the rack fault bit in the PLC5 will be cleared and the module(s) in the rack will start to update again.

With some newer 1794-ASB modules, RIUP of an I/O module is supported too. (removal and insertion under power) It is even possible with these newer modules to mask the module fault status when a it's removed under power. That can be a bad thing, depending on the application. It is usually best fot the PLC program to know when a module is missing and deal with it accordingly.

What ever you do, make sure your documents for the 1794-ASB series match the actual device series. A/B has changed the functions of some of the switches over the years to support newer processors and I/O densities, so be careful there...A series "A" user manual will not apply correctly to a series "E" module.

Hope this helps,
Paul
  Reply With Quote
Old December 17th, 2006, 11:27 AM   #3
bbear
Member
United States

bbear is offline
 
Join Date: Dec 2006
Location: ohio
Posts: 63
Thanks very much.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
How many Compact Block IO or Flex IO a SLC Scanner support? ckchew666 LIVE PLC Questions And Answers 6 August 30th, 2006 12:08 PM
PLC5 and DH+ and Flex IO dimented LIVE PLC Questions And Answers 19 May 12th, 2006 07:33 AM
AB PLC5/80B RIO Flex IO Fault corkers LIVE PLC Questions And Answers 9 September 4th, 2004 01:12 AM
PLC5 HotBackup with Flex IO Configuration Joydip LIVE PLC Questions And Answers 0 May 7th, 2002 06:22 AM


All times are GMT -5. The time now is 05:27 AM.


.