Flex IO communications fault
bbear
Dec 2006
ohio
63
I would like to ask a question about remote IO faults. I have a small project using PLC5 with a 1794 Analog Module. The analog module is the only module on this Rack. The field devices on the module are LVDT's power by an external 24vdc source with common to ground. Should the analog card be powered by the same 24vdc source as the LVDT's? The 1794-ASB could power the analog reading the publication. I would like to power the analog module from the external supply but I did not know if when the external power supply is powered down to change out a either LVDT if it would fault the ASB with an Adapter Fault of a Local Fault and/or if either would effect operation of other equipment being controlled by the PLC5. Also if a fault, would it clear when power is restored on the Analog Module or could it be cleared by the reset on the ASB?
Any help would be appreciated.
Sounds good like it is...
It is usually best to keep your I/O power supply separate from the ASB power supply. It should be okay to replace a faulty LVDT without turning off power to the analog card adapter module. In addition, you can remove power from the device side of the analog module without faulting it, and disconnect signal wires if necessary. Your analog readings will go to the minimum values, and the PLC will respond how it has been programmed when those values change.
If you power down the 1794-ASB and the PLC5 is still up and running, you will get a rack fault for that rack in the "S" status file in the PLC5. This is a minor fault which will not halt the processor. The PLC program will continue to run and the other I/O will not be affected.
The output image bits in the PLC5 for the affected modules will either be reset or hold their last states, depending on how you set the dip switches for the 1794-ASB.
The PLC can be configured to continually try to restore communication by setting the dipswitch for "allow processor restart". If that dipswitch is not set, the technician must initiate a reset of the rack to restore communication. When communication is restored, the rack fault bit in the PLC5 will be cleared and the module(s) in the rack will start to update again.
With some newer 1794-ASB modules, RIUP of an I/O module is supported too. (removal and insertion under power) It is even possible with these newer modules to mask the module fault status when a it's removed under power. That can be a bad thing, depending on the application. It is usually best fot the PLC program to know when a module is missing and deal with it accordingly.
What ever you do, make sure your documents for the 1794-ASB series match the actual device series. A/B has changed the functions of some of the switches over the years to support newer processors and I/O densities, so be careful there...A series "A" user manual will not apply correctly to a series "E" module.
Hope this helps,
Paul
I'm having communication/parameter problems trying to replace a Powerflex 700 in a centrifuge application with a controllogix PLC, version 17, and...
3,496
Hello, Current I am working on a school project involving PLCs and the PowerFlex 40 drive. The Drive is currently running though the Drive...
7,330
A/B has been touting their Micro800 Connected Components line with the ability to simply drag and drop Powerflex drives into the project but now...
2,976
I have a PLC5/40E PLC. It has a RIO network already connected to it. I want to add a Powerflex 700 with a 20-comm-r communications card to this...
6,040
Good day. We have a problem with the configuration of an Allen Bradley Powerflex 700 VFD drive. I am hoping that someone can help out with this...
5,790