Hello,
I need some help/advice. I have a Micrologix 1400 series B on surface at a mine site. Underground I need to read hart data from a flow meter. We installed the Schneider STB with hart Modules. I can see that the STB module is properly retrieving all the data from the flow meter. But my problem is getting the PLC to retrieve the data from the STB module Via Modbus TCP.

I know that the ML 1400 Series B is compatible with Modbus TCP, I enabled it in the programming and setup my message instructions. But after I toggle a bit to enable the MSG instruction I get error "Local Communication is shut down?"

I made sure to enable the Modbus TCP Features.

As for the Schneider STB module, I can connect to it remotely from surface no problem and make changes to it, as needed.

I attached two Screen shoots of the RSlogix MSG configs for the totalizer and the STB registers.

Any advice is very appreciated.

Thanks everyone
Attached Images
File Type: jpg Capture12.JPG (68.1 KB, 20 views)
File Type: jpg Capture13.jpg (76.0 KB, 17 views)
  Reply With Quote
Old April 16th, 2018, 01:44 PM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,782
Quote:
Originally Posted by richleva View Post
But after I toggle a bit to enable the MSG instruction I get error "Local Communication is shut down?"
This is (in my experience) a sure sign that you need to power cycle the PLC to get the changes to the Ethernet port to properly take effect.

Also, the node number (Unit Identifier) of 255 looks suspect. I'm not familiar with your other device, so it might be okay...some devices ignore the node number with Modbus TCP altogether since you are calling them out by IP address.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old April 16th, 2018, 01:50 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,897
RA Knowledgebase confirms; when you enable Modbus/TCP on a MicroLogix 1400, you must power cycle at least once to reset the communications stack.

https://rockwellautomation.custhelp....il/a_id/117801
  Reply With Quote
Old April 16th, 2018, 02:03 PM   #4
richleva
Member
Canada

richleva is offline
 
Join Date: Sep 2012
Location: ontario
Posts: 60
Ok Thanks Guys, I will try this tomorrow. But, when downloading to the controller. does it not cycle power on its own? Or maybe not...
  Reply With Quote
Old April 16th, 2018, 02:17 PM   #5
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,782
Quote:
Originally Posted by richleva View Post
Ok Thanks Guys, I will try this tomorrow. But, when downloading to the controller. does it not cycle power on its own? Or maybe not...
Not. It's only when making changes to the channel settings that a power cycle is required. Just changing the IP address may allow comms to keep working at least for a short while, but any changes to the port call for a power cycle. Enabling Modbus TCP and then going to run mode without power cycling has given me that same error.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old April 16th, 2018, 09:58 PM   #6
Sapper307
Member
United States

Sapper307 is offline
 
Join Date: Nov 2017
Location: Maryland
Posts: 73
Quote:
Originally Posted by OkiePC View Post
This is (in my experience) a sure sign that you need to power cycle the PLC to get the changes to the Ethernet port to properly take effect.

Also, the node number (Unit Identifier) of 255 looks suspect. I'm not familiar with your other device, so it might be okay...some devices ignore the node number with Modbus TCP altogether since you are calling them out by IP address.
its been my experience that more times than not the unit id/slave id/node id whatever you want to call it, is significant even in modbus/tcp. you may want to ensure you are using the proper slave id number in your modbus poll.
  Reply With Quote
Old April 17th, 2018, 11:14 AM   #7
richleva
Member
Canada

richleva is offline
 
Join Date: Sep 2012
Location: ontario
Posts: 60
Talking

Quote:
Originally Posted by OkiePC View Post
Not. It's only when making changes to the channel settings that a power cycle is required. Just changing the IP address may allow comms to keep working at least for a short while, but any changes to the port call for a power cycle. Enabling Modbus TCP and then going to run mode without power cycling has given me that same error.
Everything Worked Perfect after the power cycle !!!
Thank you very much
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Modbus TCP vs UDP; Modbus TCP vs RTU over RS-485 danw LIVE PLC Questions And Answers 6 March 18th, 2018 07:49 PM
Ethernet TCP/IP and Allen-Bradley CompactLogix (RSlogix 5000) CAAJ LIVE PLC Questions And Answers 14 December 18th, 2015 11:46 AM
CP341 to Kepware OPC : Modbus TCP jeffy LIVE PLC Questions And Answers 2 July 2nd, 2015 06:23 AM
Modbus Master not polling the Modbus Slave through an EtherNet/IP Connection mihiri LIVE PLC Questions And Answers 3 July 15th, 2010 02:41 AM
Mitsubishi Q Series Modbus TCP module QJ71MT91 set up help req'd... Pocko LIVE PLC Questions And Answers 0 July 30th, 2006 02:45 AM


All times are GMT -5. The time now is 07:36 AM.


.