Measuring braking resistor for future sizing.

I have been working developing winder systems for the past several years. They operate using winders running on AC induction motors and PowerFlex 755's with braking resistors sized for 110% power -- due to what I consider an overhauling layout.

I am not convinced we need braking resistors this large. On every unit I have built the resistors never get much above ambient temperature.

In an effort to optimize the system I wanted to see if there was a good way to measure how much of the braking resistor I am using in order to optimize but due to the nature of how they are used I'm not sure the best way of measuring this.

I know the DC bus is pulsed to the resistor, so I could attempt to measure voltage in those leads but I am not sure if I could capture and log quick enough for a significant amount of time.

Any ideas or suggestions would be greatly appreciated.
  Reply With Quote
Old April 16th, 2018, 10:45 AM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,833
Does your system utilize a controlled e-stop? If so, be sure to consider stopping the full load quickly in an e-stop situation before reducing the braking capability.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old April 16th, 2018, 12:10 PM   #3
Pete.S.
Member
United States

Pete.S. is offline
 
Join Date: Mar 2016
Location: Fl
Posts: 457
You already answered your own question - just measure the temperature.
  Reply With Quote
Old April 16th, 2018, 12:39 PM   #4
Lynx777
Lifetime Supporting Member
United States

Lynx777 is offline
 
Join Date: Aug 2008
Location: Indiana
Posts: 55
I asked AB's Tech Connect about monitoring DB usage a year or so ago and this is what they had to say.

"Parameter 935 bit 20 will tell you if the brake is currently on or off
As far as power use testpoint 676
dynamic brake resistor calculated power (i.e. volts * amps for a given interrupt period)
When you put the value 676 in parameter 970 [test point sel 1] the calculated value be put in Parameter 971 and 972 _ "

It worked well for what I needed.

Just an addon thought: Once you have data you want out at the parameter level you can use several methods to record the data. I've used the method above with 3rd party trending software as well as AB's own built in trend tools. I've also tied it to one of the analog outputs of an I/O option board and then set up a volt meter so that I could see what was happening while I was out testing the equipment.

Last edited by Lynx777; April 16th, 2018 at 01:38 PM.
  Reply With Quote
Old April 16th, 2018, 01:00 PM   #5
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 712
Why not use a line regeneration drive and eliminate the resistor altogether.
It will give you 100% regen 100% of the time and the energy can be used by other equipment.
E-Stops are a little different they require the drive to be in safe mode or disconnect the motor leads either way the motor will coast to stop.
It is except able to have a short time delay to E-Stop the motor at a fast rate using the drive and then when the motor is stopped put the drive in safe mode only a few seconds some safety relays have a built in timer for that purpose.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Sizing VFD recommendations einnh LIVE PLC Questions And Answers 12 May 19th, 2016 12:16 PM
PFLX70 Dynamic Brake parameters unsaint32 LIVE PLC Questions And Answers 14 December 4th, 2014 06:54 PM
Regen braking with a "backup" snubber braking leitmotif LIVE PLC Questions And Answers 29 October 9th, 2013 11:23 AM
VFD class / automotive / help with regen braking leitmotif LIVE PLC Questions And Answers 12 October 2nd, 2008 07:51 AM
Regenerative Drives craigsimon LIVE PLC Questions And Answers 9 February 14th, 2003 04:09 PM


All times are GMT -5. The time now is 10:06 PM.


.