Proper landing of shielded wire within cabinet

so ive been reading up all about proper handling of shielded signal wires, but i still have a few questions. if youre dealing with say a 4-20ma sensor in a machine, using belden 8760 cable for said sensor. that cable runs from the sensor to a junction box on the machine where there is a DIN rail with terminal blocks. once on site there would be wires pulled from the machine junction box to the control cabinet. in the control cabinet that cable would be landed directly on an analog input card.

-That shield for said cable, where would that be landed within the control cabinet? Should that go to a terminal block, the kind thats bonded directly to the DIN rail? Or is there a better method?

-Should the shield on that cable be landed in the machine junction box at all? I assume then it would be carried all the way through to the control cabinet.

lots of people on here with tons more experience then i have on this subject and im looking forward to learning how this is normally handled by the masses out in the real world. thanks!
  Reply With Quote
Old April 14th, 2018, 11:55 PM   #2
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,420
As a general rule, you should terminate the shield to ground in your PLC cabinet and cut the shield and tape the cable at the instrument end. How best to terminate to the module varies with different PLC brands and different IO modules. It is typically preferable to pre-wire analog input modules to a terminal strip that is designed to provide 24 VDC loop excitation power, if needed, and provide for shield termination along with the analog input plus and minus terminals. Some manufacturers also offer IO module faceplates with pre-wired extension cables to DIN rail mountable terminal boards. It can be difficult to terminate field wires directly to certain analog input modules.
__________________
  Reply With Quote
Old April 14th, 2018, 11:58 PM   #3
seth350
Member
United States

seth350 is offline
 
seth350's Avatar
 
Join Date: Jul 2011
Location: Over yonder
Posts: 261
Land the shield at the card on a good ground. Some cards have a terminal for a shield too.
Never land the shield at more than one ground. You can go through a terminal block if needed.

I say at the card because some people have the terminal blocks at the bottom of the cabinet for landing field devices. They land the shield there to ground and use regular unshielded wire to run through the wire duct past a VFD and through a mess of 3phase distribution wires. What noise the shield took care of getting from the field device to the cabinet is picked back up inside the wire duct.

It’s good practice to try to separate the cabinet out for clean and dirty signals as well.
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry
  Reply With Quote
Old April 15th, 2018, 12:01 AM   #4
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,420
Quote:
Originally Posted by JZerb View Post
so ive been reading up all about proper handling of shielded signal wires, but i still have a few questions. if youre dealing with say a 4-20ma sensor in a machine, using belden 8760 cable for said sensor. that cable runs from the sensor to a junction box on the machine where there is a DIN rail with terminal blocks. once on site there would be wires pulled from the machine junction box to the control cabinet. in the control cabinet that cable would be landed directly on an analog input card.

-That shield for said cable, where would that be landed within the control cabinet? Should that go to a terminal block, the kind thats bonded directly to the DIN rail? Or is there a better method?

-Should the shield on that cable be landed in the machine junction box at all? I assume then it would be carried all the way through to the control cabinet.

lots of people on here with tons more experience then i have on this subject and im looking forward to learning how this is normally handled by the masses out in the real world. thanks!
I didn't mention the JB. Generally speaking, when shielded cables pass through junction boxes, their shields should also be terminated along with the signal wires. The shield should ideally remain continuous from the PLC chassis to the instrument, where it should be insulated.
__________________
  Reply With Quote
Old April 15th, 2018, 12:04 AM   #5
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,420
Quote:
Originally Posted by seth350 View Post
I say at the card because some people have the terminal blocks at the bottom of the cabinet for landing field devices. They land the shield there to ground and use regular unshielded wire to run through the wire duct past a VFD and through a mess of 3phase distribution wires. What noise the shield took care of getting from the field device to the cabinet is picked back up inside the wire duct.
That sounds like a poorly designed control panel.
__________________
  Reply With Quote
Old April 15th, 2018, 12:12 AM   #6
seth350
Member
United States

seth350 is offline
 
seth350's Avatar
 
Join Date: Jul 2011
Location: Over yonder
Posts: 261
Quote:
Originally Posted by Bit_Bucket_07 View Post
That sounds like a poorly designed control panel.
It’s what you get when managers want a machine to do something different or add a function. Not to mention it must be complete before the next shift comes in, and anyone can go into a storeroom and check out an enclosure, some terminal blocks, din rail, and a plc. Building panels is something they say they really enjoy doing, except they do it really wrong.
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry
  Reply With Quote
Old April 15th, 2018, 01:20 AM   #7
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 188
Quote:
Originally Posted by Bit_Bucket_07 View Post
I didn't mention the JB. Generally speaking, when shielded cables pass through junction boxes, their shields should also be terminated along with the signal wires. The shield should ideally remain continuous from the PLC chassis to the instrument, where it should be insulated.
ok, so the drain wire would be landed at a terminal block in the JB normal terminal block, nothings thats bonded to ground via the DIN rail. also, i mainly work with AB I/O modules, which dont seem to have a provision to land the shield. you also mentioned cutting the shield and 'taping' the cable at the instrument end, what exactly does that entail.
  Reply With Quote
Old April 15th, 2018, 09:33 AM   #8
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,921
http://www.mouser.com/pdfdocs/alphaw...lded-Cable.pdf
  Reply With Quote
Old April 15th, 2018, 11:03 AM   #9
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,420
Quote:
Originally Posted by JZerb View Post
ok, so the drain wire would be landed at a terminal block in the JB normal terminal block, nothings thats bonded to ground via the DIN rail. also, i mainly work with AB I/O modules, which dont seem to have a provision to land the shield.
The shield wire should only be grounded in the PLC cabinet. If the JB you refer to is pre-wired to the instrument and has provisions for the shield to terminate and pass through the box, then I have to assume that the shield has been cut and insulated at the actual instrument. You shouldn't assume. You should verify.



Quote:
Originally Posted by JZerb View Post
you also mentioned cutting the shield and 'taping' the cable at the instrument end, what exactly does that entail.
When terminating the instrument end of a shielded cable, after stripping off the outer jacket, you should cut the foil/braid shield and the shield drain wire off and tape the end of the outer jacket so that the shield can't incidentally make contact with ground. A piece of heat shrink would also work for this purpose, but it's far more common to use electrical tape for field wiring.
__________________
  Reply With Quote
Old April 15th, 2018, 12:11 PM   #10
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 188
Quote:
Originally Posted by Bit_Bucket_07 View Post
The shield wire should only be grounded in the PLC cabinet. If the JB you refer to is pre-wired to the instrument and has provisions for the shield to terminate and pass through the box, then I have to assume that the shield has been cut and insulated at the actual instrument. You shouldn't assume. You should verify.
Excellent. What I currently do is in line with what you have described above aside from a few details, which could be culprits for my noise issues i tend to have. We’ve typically run the analog input module wires within the cabinet to a terminal block, then when the wiring comes in from the field land the signal wires in their appropriate spots and the shield is then attached to a green/yellow terminal block that’s bonded to the din rail. Moving forward I will bring the signal wires from the machine into the PLC cabinet and directly to the input module. I will also be more cautious when cutting the signal wire at the instrument end and making sure to tape the shield to make sure it doesn’t come in contact with anything it shoildnt. The other issue I believe I have is that we use aluminum din rail, and in another thread I found in here in my research on this subject it seems as if that’s not ideal for a proper grounding situation, better to use a steel din rail, grind the paint off the white painted steel backplane in the cabinet and go from there.
  Reply With Quote
Old April 15th, 2018, 06:25 PM   #11
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,698
The general rule is to keep the shield continuous from instrument to PLC card, and to ground it at one point only. So anywhere there's a terminal strip or a j-box or any other cable joint, the shield needs to be terminated like any other wire (except unlike a regular wire, you might need to sleeve it).

From a functional perspective, where the shield is grounded makes no difference. From a practical perspective, there are some "good practice" and "bad practice" ways of doing it.

The easiest way I find is to earth it at the PLC cabinet terminal strip, using a terminal that earths via the DIN rail. You must still use screened cable from terminal strip to PLC card. So the cable from terminal strip to instrument will have the shield connected to ground at the cabinet end, and cut and taped at the instrument end. Likewise the cable from terminal strip to PLC card will have the shield connected to ground at the terminal strip end, and cut and taped at the PLC card end. You still end up with a shield that is continuous from instrument to PLC module, and grounded at one point only.

On place I often have to deviate from this is with load cells. Many load cells have the cable screen bonded to the body of the load cell, meaning that the cable shield will be grounded at the instrument end by virtue of being bolted to the frame of a machine. This is not ideal because the machine is probably earthed by virtue of being metal and bolted to other things, but it's not deliberately earthed for the purposes of an instrument earth. So you may have to connect an earth wire to the machine for that purpose. Much easier to buy a load cell that doesn't have the shield bonded to the body and to earth it at the panel end, but of course we don't always get to call those shots.
  Reply With Quote
Old April 16th, 2018, 04:20 AM   #12
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,445
Quote:
Originally Posted by JZerb View Post
We’ve typically run the analog input module wires within the cabinet to a terminal block, then when the wiring comes in from the field land the signal wires in their appropriate spots and the shield is then attached to a green/yellow terminal block that’s bonded to the din rail.
Yeah, it something that many people do, but it is far from good enough

Quote:
Originally Posted by JZerb View Post
The other issue I believe I have is that we use aluminum din rail, and in another thread I found in here in my research on this subject it seems as if that’s not ideal for a proper grounding situation, better to use a steel din rail, grind the paint off the white painted steel backplane in the cabinet and go from there.
Even better is to use a dedicated shield clamping bar.

This is what we do:
At the cable entry at the bottom of the cabinet, there is a proper earthing bar with clamps for connecting the screens. The screens are not cut at the earthing bar. Only section of the mantle on the cable is removed to allow for good connection to the clamp. But the screen is allowed to continue with the cable right up to where the wires are connected to the final input device (i.e. the PLC).

__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old April 16th, 2018, 07:20 AM   #13
karlek
Member
Croatia

karlek is offline
 
karlek's Avatar
 
Join Date: Jul 2014
Location: Varazdin, Croatia
Posts: 63
Quote:
Originally Posted by JesperMP View Post
Yeah, it something that many people do, but it is far from good enough

Even better is to use a dedicated shield clamping bar.

This is what we do:
At the cable entry at the bottom of the cabinet, there is a proper earthing bar with clamps for connecting the screens. The screens are not cut at the earthing bar. Only section of the mantle on the cable is removed to allow for good connection to the clamp. But the screen is allowed to continue with the cable right up to where the wires are connected to the final input device (i.e. the PLC).

How do you strip the cable like that without damaging shield? Scalpel?
  Reply With Quote
Old April 16th, 2018, 07:56 AM   #14
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,895
Quote:
Originally Posted by JesperMP View Post
This is what we do:
I like it... and thats what I do also, I learned it from some German cabinets that I worked on that had a bunch of SEW drives, looked great and worked great very little noise issues


Quote:
Originally Posted by karlek
Scalpel?
Thats what I use, I like Olfa and I use blades A1160B but be careful they are sharp, I use a used one with cutting insulation
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old April 16th, 2018, 08:46 AM   #15
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,445
There are cable tools for exactly this purpose.
But I just use a sharp knife and my surgeon-like senses.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Shielded Wire Duct The Plc Kid LIVE PLC Questions And Answers 2 December 1st, 2011 12:00 PM
AWG wire sizes in the European Union TConnolly LIVE PLC Questions And Answers 4 September 20th, 2010 08:57 PM
Proper way to wire overloads Maintenance Man LIVE PLC Questions And Answers 26 November 29th, 2009 09:31 PM
Wire flexability for data collector rpoet LIVE PLC Questions And Answers 3 August 12th, 2008 11:26 PM
Do I need a shielded wire for 4-20mA signal? Cryogen LIVE PLC Questions And Answers 6 March 17th, 2006 09:24 AM


All times are GMT -5. The time now is 04:18 AM.


.