Dc drive

Having problems with a DC Drive Older BBC Veritron 10 hp that is running a 10 hp motor through a gearbox 5:1 ratio and drives a conveyor flat belt.
It seems the drive has no "balls" when the load increases on the belt and just stops. after a few minutes then it will trip the overload which I believe is on the armature leads (only one) I replaced the motor, checked the gearbox, and inspected the bearings on the belt it drives. I get no fault at drive or at least nothing I can see. Is it possible the drive is just failing (30 years) I am getting one in hopes of solving this but still am not convinced its the drive. Motor does not get hot, when gearbox is released from belt it will run with no load.
Any Ideas, Thanks
__________________
B.Pedersen
if you are going to assume, assume your wrong.
  Reply With Quote
Old April 16th, 2018, 07:40 PM   #2
jrwb4gbm
Lifetime Supporting Member + Moderator
United States

jrwb4gbm is offline
 
Join Date: Apr 2002
Location: NC
Posts: 2,201
If this motor has a separate field supply, verify that it is working properly and supplying the right voltage. I don't know if you used a new motor or a spare used one but if it was a used spare motor and uses a PM (Permanent Magnet) field, after 30 years the magnetism in the field could be weaker than needed.
A bearing on the conveyor may also be bad. It might be best to just replace them.

Last edited by jrwb4gbm; April 16th, 2018 at 07:46 PM.
  Reply With Quote
Old April 16th, 2018, 08:03 PM   #3
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 212
Without verifying the armature current with a DC ammeter, it's impossible to tell what's going on. The armature current is directly proportional to torque. The drive may be supplying full current.

Also measure the field current and voltage to determine if it is getting the proper excitation. The stronger the field (Watts / Ampere Turns), the higher the Kt (FtLb/Amp), Also, the lower the Ke (RPM/V). It's like a gearing change.

It could be that you have a partially shorted field, and a current regulated field supply. In which case, the voltage on the field will be low, but the current correct. If it's a voltage regulated or fixed (diode bridge) field supply, the voltage will be correct, but the current high.

You cant really troubleshoot a DC drive without a DC ammeter...
  Reply With Quote
Old April 16th, 2018, 08:24 PM   #4
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 625
Sounds to me like you lost the field power supply with out a filed the motor can't develop torque but it will overload the current in the armature and trip the overloads.
Verify the field supply if it's not there replace the hole thing with a good VFD and you don't have to be concerned about it. AC VFD is always better then a DC now
  Reply With Quote
Old April 16th, 2018, 10:41 PM   #5
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,421
Quote:
Originally Posted by GaryS View Post
.... AC VFD is always better then a DC now
Oh oh ... you've opened the floodgates now...
  Reply With Quote
Old April 17th, 2018, 12:14 AM   #6
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 625
Anything you can do with a DC drive system I can do with an AC drive system and a lot more.
I would welcome that discussion anytime There are many advantaged of an AC drive over DC.
  Reply With Quote
Old April 17th, 2018, 02:42 PM   #7
roxusa
Lifetime Supporting Member
United States

roxusa is offline
 
Join Date: Nov 2008
Location: NJ
Posts: 355
I swapped the drive with an identical one from another line and had the same problem.
The next shift came in and the mechanic said even though this motor was sent out for repair its the same problem he had with it on the other line that is why he changed it. He put the original one back that was giving sporadic problems and it has ran 2 shifts without problems, I sent the motor back to motor shop (OEM Upgrade is to replace Motor/Gearbox and Drive to AC & VFD) I only need 1 more year on this and I have new machine coming. Hope they find something at the Motor Shop.
thanks
__________________
B.Pedersen
if you are going to assume, assume your wrong.
  Reply With Quote
Old April 17th, 2018, 02:53 PM   #8
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 625
from what you say it looks like you have a wiring problem. A loose connection on the motor field wiring. Check the current in the field a Clamp On DC Meter will work Current in must = current out. it also must be with in the current range specified on the motor name plate
I the both the motor and drive have swapped out with known good then the problem must be in the wiring
  Reply With Quote
Old April 17th, 2018, 02:57 PM   #9
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,615
Quote:
Originally Posted by jraef View Post
Oh oh ... you've opened the floodgates now...
Quote:
Originally Posted by GaryS View Post
Anything you can do with a DC drive system I can do with an AC drive system and a lot more.
I would welcome that discussion anytime There are many advantaged of an AC drive over DC.
I think that there are fewer arguments today than 10-15 years ago about the advantages of DC drives/motors.

I am just glad I no longer have to polish commutators and do PMs on brushes.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old April 17th, 2018, 03:27 PM   #10
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 212
Let us know what they find. My money's on the field windings...
  Reply With Quote
Old April 17th, 2018, 03:30 PM   #11
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 212
Quote:
Originally Posted by GaryS View Post
Anything you can do with a DC drive system I can do with an AC drive system and a lot more.
I would welcome that discussion anytime There are many advantaged of an AC drive over DC.
360hz noise is hard to produce with an AC drive

For the most part, I agree. It's difficult sometimes to fit an AC motor in the limited space a DC motor used to fit, but usually it's not an issue.
  Reply With Quote
Old April 18th, 2018, 09:18 AM   #12
roxusa
Lifetime Supporting Member
United States

roxusa is offline
 
Join Date: Nov 2008
Location: NJ
Posts: 355
My DC motor has 4 field wires marked f1-f2-f3-f4 and the wire diagram shows f2 &f3 wired together with my leads on f1 & f4. If they marked this incorrectly and I only had half of the field energized would I experience these symptoms. I didn't check the continuity before sending it back to motor shop. Just a thought
__________________
B.Pedersen
if you are going to assume, assume your wrong.
  Reply With Quote
Old April 18th, 2018, 09:31 AM   #13
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 625
What dos the motor name plate show. i would bet it's a dual voltage field 250 -500 VDC
f1-f2 is one winding f3-f4 is the other. 500V wire the windings in series. From your description I would think its a 500V winding. the most important thing with the field is the current at rated field current the motor RPM max is base speed then you go into field weakening for extended speed ( speed above base speed) for field weakening you lower the field voltage this lowers the field current
Most DC motors show the field as voltage and min - max current
if you have no field current the motor will not develop torque
  Reply With Quote
Old April 18th, 2018, 09:35 AM   #14
roxusa
Lifetime Supporting Member
United States

roxusa is offline
 
Join Date: Nov 2008
Location: NJ
Posts: 355
This is what I have, Thanks
Attached Images
File Type: jpg IMG_6216.JPG (111.8 KB, 44 views)
__________________
B.Pedersen
if you are going to assume, assume your wrong.
  Reply With Quote
Old April 18th, 2018, 09:51 AM   #15
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 625
There you have it 500V armature volts
Field 300/150 V
i can't quite read the field ohms
measure the ohms in the field from the drive side it should be close the plate value
don't forget series parallel resistance of the field winding in your case the windings are in series
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Looking for Fincor 2255 DC drive wiring diagram Mbeavers34 LIVE PLC Questions And Answers 2 January 13th, 2010 07:16 AM
Drive Monitor DC masterdrive Siemens Arun LIVE PLC Questions And Answers 1 January 19th, 2008 08:35 AM
DC Drive replacement scottmurphy LIVE PLC Questions And Answers 6 May 25th, 2005 10:01 PM
Automax DC drive Card Configuration. dao LIVE PLC Questions And Answers 6 December 2nd, 2003 06:45 AM
6RA 27 dc main spindle drive ushakkal LIVE PLC Questions And Answers 0 September 15th, 2003 11:52 PM


All times are GMT -5. The time now is 02:09 AM.


.