Modbus RTU connection from a Micrologix 1400 to Accuvim iiR-D
sophickj
Nov 2015
Jamaica
I need some assistance in establishing a modbus RTU connection (communication) with a Micrologix 1400 and a accuvim ii. An AIC was used to connect from the accuvim ii to the PLC but I am not getting a connection. Anyone familiar with this process can assist please.
The 1761-AIC+ is a RS232 to RS485 converter/isolator and a point to point RS232 isolator. See manual below (page 10). It will work for the OP's application.
https://www.google.com/url?sa=t&rct...S6EO3n7Y_amsAQaQg&sig2=4WAlI984E3LCm5t7DzPAmQ
But channel 0 can be setup for RS485 communication without using an AIC, see excerpt from the manual for the ML1400 below.
When connecting to RS-485 network using DH-485, DF1 Half-Duplex Master/Slave,
Modbus RTU Master/Slave or DNP3 Slave protocols, the MicroLogix 1400 can be
connected directly via Channel 0 without an Advanced Interface Converter, catalog
number 1761-NET-AIC. The Channel 0 combo port provides both RS-232 and
RS-485 isolated connections. The appropriate electrical interface is selected through
your choice of communication cable. The existing MicroLogix 1761 communication
cables provide an interface to the RS-232 drivers. The 1763-NC01 cable provides an
interface to the RS-485 drivers.
I am not familiar with the OP's Accuvim iiR-D
Just working on a job with a heap of Schneider power monitors connected to my PLC with Modbus RTU. There are the usual D0 and D1 connections...
2,231
Hi! Greetings, I've been trying to use the PLC M221 to control and read the variables from the VSD ATV312 through Modbus RTU, which is something...
1,601
Hello, I'm a newbie to PLC's and network protocols, and I need your help with setting up a modbus rtu network. Hardware 1: Micrologix 1400...
12,171
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
45
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
204