Old July 30th, 2020, 10:24 AM   #31
rzuhair
Member
United States

rzuhair is offline
 
Join Date: May 2019
Location: Houston
Posts: 7
Quote:
Originally Posted by drbitboy View Post
So the supplier says "it was working to spec when we leased it to you, you broke it you pay to fix it."


Is that it?
Correct.
  Reply With Quote
Old July 30th, 2020, 12:28 PM   #32
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,214
In that case, going back to the OP, I would suggest the PLC
  1. Set pump speed via a fixed frequency value e.g. 60Hz
  2. Control pump outlet pressure rise, measured between the pump and a valve downstream of and near the pump outlet, to the middle of "efficiency" range, using that same valve
  3. Measure the flow
Notes


  • Only one PID loop is required.
  • A measured flow greater than or equal to the flow for that speed and pressure means the pump meets the specs.
  • Several speeds could be used, as well as several pressures, but the "meets spec" metric is always the same (see next item below also)
  • It may be easier to control flow and measure pressure rise, in which case "meets spec" is a pressure rise less than the curve at the frequency and flow.
  • The measured pressure rise is between the pump outlet and the pump inlet, so if the pump outlet pressure is measured as PSIG wrt atmospheric, then any head in the sump above the level of the pump inlet must be subtracted from that measurement and used in the control.
  • Flow measurement is by nature one of the lowest-accuracy measurements, so it may be the source of debate with the customer. There are at least two ways to handle this:
    • Simplest: Make the meets/doesn't-meet flow number some percentage less than the curve.
    • Messy but eliminates any dispute over flow measurement: if the flow is small enough it may be possible to fill the sump and not recirculate the water, and convert a sump level change over time into a flow, or even use a time between two levels as the spec; this may change the outlet pressure, but that can be handled by integrating a sump level sensor into the measurement of the control variable.
  Reply With Quote
Old July 31st, 2020, 10:15 AM   #33
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 6,071
You are making life tougher than it needs to be. No PID or control is required.

If you are looking to verify that impeller wear or other mechanical damage hasn't caused excessive drift from the manufacturer's performance curve just plot flow vs. pressure at 60 Hz (or whatever the manufacturer's original curve used for the base curve) and compare.

1) Pick 5 to 8 points flow and pressure points off the original curve and put them in Excell
2) Run the pump at the base speed and using a valve create backpressure. Measure pressure (suction) at the pump suction and discharge flanges (or as close to them as possible.) Make sure you have the same diameter pipe at your measurement point as the pump flange to avoid velocity head changes. You need both pressure measurements because the original curve is undoubtedly delta p across the pump. Measure the flow at that total pressure rise.
3) Repeat step 2) 4 to 7 times and put the points in the Excel spreasheet.
4) Use the Excel data to chart the original points with the curve and the new points without a curve. Use the trend function on the chart to plot the best fit curve for the test data - generally a polynomial. That gives you a smooth curve if the data has some scatter.
5) If the two don't line up within accepable limits send an invoice.

Last edited by Tom Jenkins; July 31st, 2020 at 10:17 AM.
  Reply With Quote
Old July 31st, 2020, 12:24 PM   #34
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,214
Quote:
Originally Posted by Tom Jenkins View Post
You are making life tougher than it needs to be. No PID or control is required....

Tom is exactly right, of course; my suggestion over-complicates the issue.


OT (but related, it's been that kind of Friday ...):



When testing large steam turbines (half a gigawatt and up, IIRC), my Dad (metioned twice on one day, and still another half a dozen threads to go, how about that?) said GE would run what they call a "valves wide open" test - isolate the process (turbine), open the inlets steam, and measure everything ASAP after commissioning to get a baseline (also to prove the as-built turbine meets the contract heat-rate, Btu/kWh, to ensure the final payment from the customer is made). Basically they treat the turbine as a flow element, analogous to an orifice meter or other pressure-drop flow measurement element.


Later, when the same valves-wide-open test is run and if the results are changed from the baseline, then something in the process changed (erosion, scale built up on the buckets, whatever).


With enough measurement data they could actually pinpoint where the changes occurred, at which point you can plan activities for the next maintenance an actually estimate an ROI. They could measure turbine performance to an absolute accuracy of around a quarter of a percent, so this metric was fairly useful.
  Reply With Quote
Old July 31st, 2020, 01:07 PM   #35
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: Vancouver, WA, US
Posts: 7,184
This is making more sense now. At first there was talk of a VFD and changing speeds. The motor efficiency would change as a function of speed. Now the speed appears to be fixed at 60Hz. So is the VFD necessary to make sure the RPM is exactly 60Hz? If the pumps are not usually controlled by a VFD then there will be a little frequency droop. Shouldn't that be taken into account?





The problems I see is if there is a valve that is changing the system curve then how does one make sure the valve position and resulting system curve repeatable?


It seems there needs to be a known good pump that must be run from time to time to make a standard to which the pumps that are being tested can be compared.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old July 31st, 2020, 01:48 PM   #36
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,214
Quote:
Originally Posted by Peter Nachtwey View Post
It seems there needs to be a known good pump that must be run from time to time to make a standard to which the pumps that are being tested can be compared.

Not necessarily: Tom suggested half a dozen points or so; from that a curve can be plotted and compared to the design and/or baseline curves. If the valve is not at the exact same positions it won't matter: it is the pump's performance curve at "X" Hz that matters, and that is being compared; the system curves' values at specific valve positions are not needed.
  Reply With Quote
Old July 31st, 2020, 05:53 PM   #37
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 6,071
Here is an example of a blower project I did several years ago comparing before an after tebuild test results. (The red and blue curves are at different air temperatures.)
Attached Images
File Type: jpg Capture.JPG (107.8 KB, 19 views)
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
DP Control of a pump grnick50 LIVE PLC Questions And Answers 6 September 27th, 2015 06:25 PM
Pump pressure control loop with flow limiting RonJohn LIVE PLC Questions And Answers 14 September 9th, 2015 08:40 PM
Sump Pump Control lefeverj LIVE PLC Questions And Answers 2 May 18th, 2015 12:22 PM
How to use a PID to control a PUMP Speed dahmanishelly LIVE PLC Questions And Answers 12 June 11th, 2013 05:04 PM
Level Control PID for Duty & Assist Pumps MorphuisOGrady LIVE PLC Questions And Answers 10 March 19th, 2010 07:27 AM


All times are GMT -4. The time now is 08:45 PM.


.