Anyone familiar with an electrode well?

I'm looking at bidding what seems to be some standard pump controls for a local levy. The one thing that is giving me a bit of grief is this part of the system called "an electrode well". I was wondering if anyone could shed some light on that, as my google-foo has failed me.
  Reply With Quote
Old July 24th, 2020, 11:41 AM   #2
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 154
WAG - a perforated pipe with an electrode inside.

The pipe protects the electrode, but isn't electrically connected to it, so the rectifier power supply current pulls whatever is in the water and plates it on the electrode, cleaning the water.

It might be that the well is charged (not the tank wall) and the current flows from it to the electrode cleaning the water inside it, as the water flows through it.
  Reply With Quote
Old July 24th, 2020, 11:45 AM   #3
TWS
Member
United States

TWS is offline
 
Join Date: Nov 2007
Location: virginia
Posts: 224
without seeing the plans and specifications, I would think maybe a level probe in a stilling well. https://www.drexelbrook.com/about-us...ds/bw-controls.
You need to provide more information.
  Reply With Quote
Old July 24th, 2020, 12:11 PM   #4
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 154
Found this about an electrode well for getting gas or fluids out of fractures.
  Reply With Quote
Old July 24th, 2020, 01:46 PM   #5
saultgeorge
Lifetime Supporting Member
United States

saultgeorge is offline
 
saultgeorge's Avatar
 
Join Date: Jul 2015
Location: Detroit
Posts: 334
Hi, we had sacrificial anodes in a perforated pipe in our drinking water reservoirs when I worked for a water utility. Sort of like the ones that I saw on ships welded to the hull. The marine folks called those "zincs". They prevent electrolysis and therefore erosion and decay of metal parts submerged in treated water or salt water.
__________________
"It's better to be on the ground wishing you were flying than flying wishing you were on the ground."
  Reply With Quote
Old July 24th, 2020, 01:56 PM   #6
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 1,050
Pretty sweet 1960s hand drawn prints.
Attached Images
File Type: jpg Screenshot_20200724-125535_Adobe Acrobat.jpg (80.7 KB, 149 views)
  Reply With Quote
Old July 24th, 2020, 01:57 PM   #7
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 1,050
I'm thinking they might just be some sort of conductivity level sensor.
  Reply With Quote
Old July 24th, 2020, 03:02 PM   #8
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 154
Sparkie's right

That electrode pointed to is the lead pump start probe.

The term Electrode Well is their terminology for the grounded tank.
  Reply With Quote
Old July 24th, 2020, 04:32 PM   #9
TWS
Member
United States

TWS is offline
 
Join Date: Nov 2007
Location: virginia
Posts: 224
these folks will have everything you need: https://lumenite.com/.
  Reply With Quote
Old July 24th, 2020, 04:35 PM   #10
TWS
Member
United States

TWS is offline
 
Join Date: Nov 2007
Location: virginia
Posts: 224
Electrode well is a stilling well. like this:https://library.e.abb.com/public/7f7...S_STW-EN_C.pdf.
  Reply With Quote
Old July 24th, 2020, 10:02 PM   #11
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,969
In this context is is a stilling well, a pipe in which the electrodes hang that will not allow turbulence in the well to disturb them and make them hit each other. From this diagram though, they indicate that the electrode well is grounded, so it must be made of a conductive material. The relays appear to be inductive, like BW or Warrick, and in those systems the other part of the inductive circuit path is the grounded walls. If the probes are in a grounded metal tank, the still well can be plastic, but if not, use a metal pipe as the still well.
  Reply With Quote
Old July 25th, 2020, 02:51 AM   #12
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 1,062
Think it might be time to suggest an update to their standards! Maybe an additional service you can offer...

Omron do a floatless level switch which we use a lot over here. 61F is the start of the model number then pick what suits the application. They do electrode holders as well. Very easy to install into a DN100 PVC pipe if you need a stilling tube.

Is this fresh water or waste water? Conductive probes can be a real PITA if it's wastewater. They will develop a layer of fat and grease or get a rag wrapped around them if not regularly checked and cleaned. I prefer either a wastewater grade hydrostatic level sensor or a radar like the Endress FMR20.

If they will consider an alternative tender as well as a complying one, you can do this very easily with a PLC or RTU.

Our standard pump controls are primary RTU or PLC using an analog probe of some kind (dependent on client) and then a backup controller using float switches which we either just implement with relays or a little Zelio smart relay.
  Reply With Quote
Old July 25th, 2020, 07:32 AM   #13
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 1,050
Thanks for all the information. Man, I want to bid this, but I will only have a whole day to bid in the entire project, and I have not been able to do a site visit. We just found out about this Friday, and not being familiar with what needs to happen with those level sensors worry's me a bit. There are also a couple motorized valves that actuate with the two 125 HP pump motors that I'm not quite familiar with.



Too bad. This is a good little job, but without a site visit to get eyes on what I'm looking at, I don't think I can work up a bid in a day.
  Reply With Quote
Old July 25th, 2020, 10:57 AM   #14
g.mccormick
Lifetime Supporting Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 732
Why would they use conductivity sensors and not just an ultrasonic in a stilling well?

You could bid it with specifing ultrasonics in stilling well. Multiple sensors in multiple wells for redundancy.

Valves. Motorized butterfly valves are readily available.

Valworx are typically quick to get.
  Reply With Quote
Old July 29th, 2020, 01:23 AM   #15
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 1,050
I don't think that they had ultrasonics for this purpose back in the 60's when this system was built. The reason issue here is time. With all of that niche instrumentation, plus the standby power system needing retrofit, and no time to do a site visit, there is no way I could possibly bid this project. No way I'm walking into something like that without first putting some eyes on it.


Thanks everyone for all the information. I did learn a lot here.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Familiar with SLC, Control Logix, not so much... sparkie LIVE PLC Questions And Answers 10 June 23rd, 2015 05:01 PM
Using conductive electrode as input kallileo LIVE PLC Questions And Answers 10 April 5th, 2012 09:30 PM
Not Familiar With Siemens C7- 633 rob68r LIVE PLC Questions And Answers 0 December 17th, 2005 11:54 PM
Contrlling the height of electrode. kiran LIVE PLC Questions And Answers 6 July 30th, 2003 10:33 AM
How many PLCs should a PLC programer be familiar with? longshot LIVE PLC Questions And Answers 16 July 28th, 2002 11:52 PM


All times are GMT -4. The time now is 07:56 PM.


.