I am wiring an Omega CDE-1202 conductivity probe with a CDTX-1203 transmitter into a ML1100 via the 1762-IF4 analog input module.
I have the transmitter working correctly, but I am unsure about the analog outputs of the transmitter to the inputs of the ML1100
The transmitter has a terminal block with 4 spaces 20VDC COM COM 4-20mA
I wired the system like the 1762-IF4 manual says to do for 4 wire transmitters, but my signal in the processor is not changing. Here is what I have 20 VDC and COM from a power supply and COM and 4-20mA to the –IN0 and +IN0. Note: Both COMs are the same potential.
In the processor I have the IF4 analog input cards in Module 3 and 4 space and configured for 4-20mA and Raw/Proportional Data Format. I am using a SCP instruction to try and scale with parameters. The SCP information is Input I:3/0 Input Min. 6241 and Input Max. 31206 Scaled Min. 0 and Scaled Max. 1000 output N10:0
When I put the probe in tap water the transmitter shows a reading of 423 uS/CM and the SCP shows an output of -371. When I remove the probe from tap water the transmitter reads 30 uS/CM, but the SCP output does not change.
Any help appreciated.
Ken
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
1,183
Hey guys, I've only dealt with wiring 4-20mA analog inputs as the majority of instruments I've used are 4-20mA. I'm using a Mitsubishi VFD and...
1,152
I am trying to wire four analog signals to a analog input module AI 4xU/I 2-wire ST (6ES7134-6HD00-0BA1). When I turn on the first device...
6,661
Could someone show me an example on how to wire the analogic input for lets say channel 0 ?? Ive found this manual...
5,226
Hi All, Probably and easy question for some but I am struggling, so any help appreciated. I have an AB analog input module number is 1794-IF8IH...
5,044