whatis the standard colour wire for wiring a plc to other circuits in canada . would
it be ok to use the following if it is documented in the wiring diagram.
inputs : orange outputs : purple
0 volts : blue 24 volt : brown
In an E-Stop condition I need to maintain pwr to the plc ,can I take the power supply through a breaker before the main contactor and cut off the 24v comm to the output of the plc. what colour should I use from the safty relay to the plc if the common is 24v (pnp)I was using yellow from the relay and yellow for the common .
also if the plc is (npn) what colour should I use
for the output common
thanks
this site is great learning a lot
it be ok to use the following if it is documented in the wiring diagram.
inputs : orange outputs : purple
0 volts : blue 24 volt : brown
In an E-Stop condition I need to maintain pwr to the plc ,can I take the power supply through a breaker before the main contactor and cut off the 24v comm to the output of the plc. what colour should I use from the safty relay to the plc if the common is 24v (pnp)I was using yellow from the relay and yellow for the common .
also if the plc is (npn) what colour should I use
for the output common
thanks
this site is great learning a lot