Hello,

Has anyone experienced the following:
Putting PLC (CompactLogix) in the Run mode works fine, but switching then the key to REM throws an IO fault. The fault can be reset through PLC and then can put in the PLC in RemRun and the system runs.

IO Major/Minor revs of match and set to Compatible mode.

Thank you.
 
Maybe you have the I/O box checked in the minor fault tab of your controller properties? I'm assuming you are not getting a major fault and the PLC is completely stopping. See attached picture.

Capture (7).PNG
 
Maybe you have the I/O box checked in the minor fault tab of your controller properties? I'm assuming you are not getting a major fault and the PLC is completely stopping. See attached picture.

Unfortunately, it is the major fault that I am getting, and it does stop the controller. I can however immediately reset it.
 
In every I/O module's configuration applet, there is a Connection tab (the second from the left) with a check box labeled "Major Fault On Controller If Connection Fails in Run Mode".

That's probably what is generating your Major Fault.

The underlying reason for the I/O connection failure will be determined by the status of the connection.

Sometimes it's a defective module, sometimes it's a bad configuration, sometimes it's a firmware bug.

Look at the I/O connection status and screenshot or describe it.
 
In every I/O module's configuration applet, there is a Connection tab (the second from the left) with a check box labeled "Major Fault On Controller If Connection Fails in Run Mode".

That's probably what is generating your Major Fault.

The underlying reason for the I/O connection failure will be determined by the status of the connection.

Sometimes it's a defective module, sometimes it's a bad configuration, sometimes it's a firmware bug.

Look at the I/O connection status and screenshot or describe it.

Somehow it stopped failing without changing anything. The faults in the logs are as per attached.

pic1.png pic2.png
 
That particular code (Type 3 Code 23) is very often caused by a loose or damaged 1769-ECR End Cap. Check yours carefully.

Otherwise, be sure to check your I/O connection status if you get another fault, and you can try to narrow down which modules (in the backplane or on the network) are the root cause.
 

Similar Topics

I have a Control Logix PLC and Safety PLC , 5581ES and 55L8SP respectively, pulled out of a cabninet connected to a Panelview Plus connected over...
Replies
2
Views
1,557
Hi, I am curious to know what will happen to a Running 1756 ControlLogix L73 controller if the keyswitch is changed from Remote Run to Program...
Replies
3
Views
1,602
Hi all, I need to bring in a single AI (temperature) from a remote location (2 miles) into a Controllogix PLC. Any simple cheap suggestions...
Replies
18
Views
900
I have a project where I will need around 20 IO cards. I'll probably have 5 on a compactlogix L320ER and 15 or 20 on a Point IO AENTR module. The...
Replies
4
Views
963
Hello everybody, I have a vendor system that has some remote monitoring (read only) and remote control (read/write) data that is available via...
Replies
7
Views
2,857
Back
Top Bottom