plcbeginer1
Lifetime Supporting Member
OP
Good Day George,
The problem appears to be with one of the fiber optic cables as you had suspected (thank you!).
Module #4 which is powered only on one side does not have any light coming from it and when modules 5&6 are plugged into it (module 4)the red light stays on (module 5&6 and the error from module SDNL M1 indicates that there is a problem after module 4, three flashes followed by 4 flashes, which seems to make sense.
In an attempt to go forward, I by-passed module 4 and the red light on module 5&6 goes out. I will revisit module 4.
Now there seems to be a definite problem after module 7 which is also verified by the amount of flashes coming from the SDNL (#M1) module.
I am swapping the 7&8 modules currently which both are SNNE-0404-007 versions.
So, there appears to be a problem with module 7 or 8 and or the fiber optic cable(s)
This might take me a day or two, since I must attend to other duties as well.
ps I looked at the I/O-ASSISTANT-KABEL-PICONET No.6824399)and it seems that it is intended for other Piconet devices. (Is that the case?)
Also, is there software that goes with the cable?
Thank you for all your help!
Grant
The problem appears to be with one of the fiber optic cables as you had suspected (thank you!).
Module #4 which is powered only on one side does not have any light coming from it and when modules 5&6 are plugged into it (module 4)the red light stays on (module 5&6 and the error from module SDNL M1 indicates that there is a problem after module 4, three flashes followed by 4 flashes, which seems to make sense.
In an attempt to go forward, I by-passed module 4 and the red light on module 5&6 goes out. I will revisit module 4.
Now there seems to be a definite problem after module 7 which is also verified by the amount of flashes coming from the SDNL (#M1) module.
I am swapping the 7&8 modules currently which both are SNNE-0404-007 versions.
So, there appears to be a problem with module 7 or 8 and or the fiber optic cable(s)
This might take me a day or two, since I must attend to other duties as well.
ps I looked at the I/O-ASSISTANT-KABEL-PICONET No.6824399)and it seems that it is intended for other Piconet devices. (Is that the case?)
Also, is there software that goes with the cable?
Thank you for all your help!
Grant