1734-OE2C Series A (or B) install into new 1734-AENTR system?

HJTRBO

Member
Join Date
Jul 2008
Location
Melbourne
Posts
618
Hi all,
I have old 1734-OE2C series A and B parts knocking around gathering dust. A customer would like one installed on their machine because they like the price.
Their existing system has a 1734-AENTR (Series A Rev 3.001) adaptor set up and is working with multiple modules already installed in the chassis.
I'm not sure if the old cards will work in this system due to the age difference. I found this post from Ken Roach. I'm taking it that series A or B IO modules for a 1734-AENT(R) adaptor will not work?
 
Last edited:
Based on the datasheet (found here: http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1734-in002_-en-e.pdf) you must use rev. C modules for EtherNet. Your A and B cards would only work on DeviceNet and PROFIBUS.

------------------
Before You Begin
You can use these Series C modules with DeviceNet and PROFIBUS adapters. If you are
using RSLogix 5000 software, version 11 or higher, you can also use the Series C modules with ControlNet and Ethernet adapters.
-----------------------
 

Similar Topics

I'm trying to install a 1734-OE2C (F/W 1.003) analog output module with a CompactLogix L16 and the module is coming up with a yellow triangle...
Replies
7
Views
2,761
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
5
Views
218
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
Replies
3
Views
211
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
8
Views
333
Hi all, This is my first time working with a 1734-IE2C analog module. I am tasked with wiring the flow meter into the analog card and the OEM is...
Replies
2
Views
155
Back
Top Bottom