I've been using RSLinx 2.54 ever since we started using the Micrologix 1400. Today I installed a ML1400 on an existing Ethernet IP Network (all ML1100s previously), and downloaded my program to the processor over the Serial connection to start.

Now RSLinx is telling me that the ML1400 (1766 L32BWAA) is an unrecognized device, but it knows that it is a 1766-L32BWAA B/10.00, when I view the network over Ethernet/IP. This is the first ML1400 I've tried to program/monitor over Ethernet, usually just use the Serial connection.

I'm currently downloading RSLinx 2.57, will take about an hour, but I was just curious if this is the solution. Seems odd that the Serial connection would recognize the processor but the Ethernet connection wouldn't.

(My TechConnect contract is only 8-5, so I can't call them today).
 
Just a WAG but what about the EDS file?

I didn't know where to look on the AB Website to find it, and under downloads for the ML1400, RSLinx 2.57 was right there.

I just noticed something. It says in RSlinx:
1766-L32BWAA B/10.00

I don't think Revision B exists on the ML1400... that's odd.

I have rebooted my computer and checked the ethernet connections, but I haven't restarted the processor yet. I probably should cycle power on it once and see.

Edit:
False alarm. It's actually Series B, not Rev B.

Edit2:
Updating RSLinx seems to have worked. It's odd that the Serial connection worked, but not the Ethernet. I assumed that the EDS for the ML1400 would contain both, not one or the other. (So either both or neither would work).
 
Last edited:
I also found out where on the website the EDS files were stored. I was trying to find it through the Micrologix 1400 page, under Software and Firmware. But it is in an entirely separate category, from the main page clicking "Tools and Resources" will lead you to the EDS finder.
 
When you start to download the program, turn off the automatic ip address assignment bit in the configuration ( i don't have the laptop right now). When you download the program through the serial port, you establish the program basics.

You then reboot the plc and run "BOOTP" from your laptop.
Bootp will then work its magic and give you the mac address of the processor. you then can assign the ip address to the plc.

rslinx will then recognize the plc through the ethernet.

that's what i had to do 2 months ago.

regards,
james
 
RA quietly rolled out MicroLogix 1400 Series B this month. Among the enhancements I've seen is support for Modbus/TCP on the Ethernet port, so I'm not surprised there's all-new Ethernet firmware including a new EDS file.

New features in Series B: Knowledgebase Article ID 158069
Series A firmware support: Knowledgebase Article ID 115431
 
Also, the MicroLogix EDS files might have a wandering path from the MicroLogix product page, but they are also on the main RA EDS server with all other EDS files:

http://www.rockwellautomation.com/resources/eds/

Just enter "EtherNet/IP" as the network and "1766" as the part number and both the Series A (v1) and Series B (v2) files will appear in the search results.
 

Similar Topics

Hi everyone, I can ping our Micrologix 1400 but the problem is I can't see it on RSLinx, I already set the RSLinx to detect the PLC IP address...
Replies
6
Views
2,497
Hi, I am working with a Micrologix 1400 model 1766-L32BXB. With no input wires connected to the “in12” thru “in19”, I am getting 24 volts while...
Replies
4
Views
172
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
Replies
4
Views
241
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
484
I'm not super familiar with the Micrologix line of processors, but I am pretty familiar with RSLogix 500. I'm trying to simply copy a string to...
Replies
4
Views
260
Back
Top Bottom