Hello everyone, great site as always. When it comes to sizing a disconnect for a motor control panel, I have seen several websites with many different answers. The most common answer that I found is to size the disconnect 115% greater than the total FLA of your motors. Is this true? I have an application, small panel, with two VFD's and a PLC. They will be controlling 2 7.5H.P 480VAC motors. So just a summation of the FLA between the 2 motors, and multiply by 115% for my main disconnect? (of course also taking into account for other circuitry in the panel.).

TIA for the help,

Greg
 
Paraphrasing UL 508A sec 30.3.3 for a molded-case switch it should be not less than 115% of the FLA ratings of all motors plus the full load current of all other loads

and

the locked rotor current of the switch shall not be less than the sum of the locked rotor currents of all motors plus the full load current of all other loads
 

Similar Topics

Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
332
Good afternoon PLCS.net! I have a very odd situation that is happening, and hoping someone has some insight. We have just laid out a new 10G...
Replies
3
Views
662
This question is about a Q68TD-G-H01. When I disconnect the thermocouple connected to channel 8 of the module, I am expecting D111.F to go TRUE...
Replies
12
Views
3,439
For those of you that design / build panels: Do you typically provide a fuse / circuit breaker on your main disconnect inside the panel? We...
Replies
16
Views
5,081
Looking for recommendation for VFD's with Integral Line Side Disconnect and Fuse. 15HP Booster Pump application. I see Danfoss makes their Aqua...
Replies
11
Views
3,985
Back
Top Bottom