Hello,
I have a flowmeter capable of producing up to 250,000 pulses per minute, and am wondering if I can use this meter with my PLC.
Is a 100 khz pulse channel 100,000 pulses per second, 6,000,000 pulses per minute? If yes, then I assume my flowmeter is correct.
All I can ascertain from the controller Reference Manual, is that I have 100 khz per channel 6 total pulse inputs.
Any help is appreciated,
Tim
100KHZ = 100,000 pulses per second X 60 = 6,000,000 pulses per minute.
however, you must consider the following:
is the flowmeter compatible with the input, output type of the flow meter, distance from the meter to the plc, range you are measuring. i had an application with a flowmeter that worked great until the flow rate got below 20 gpm.
regards,
james
Thank You James.
I "think" the meter will function :)
I will pay very close attention to the distance from the meters to the PLC. My guess is it will be about 40 feet of wire per channel. I will use shielded cable.
I'm glad 100 khz is what I thought it was! Thanks for clarification.
Regards,
Tim D
Does the 1100 only have 1 high speed counter, but it can have multiple inputs? And so then the 1400 has 6 HSC and you have a choice of multiple...
1,714
Hi! Last few I've been trying to send message from MicroLogix 1400 to Micro 850. Unfortunately every time I failed :banghead:. Did someone tried...
3,177
Hello, There was a mix up in information on some redeployed equipment and two of the micro 1400's that came in were hooked to 120v when they...
1,947
I am trying to exchange data (N registers) to and from a Control Logix PLC. I am programming the messages in the Control Logix program, to...
2,147
Error: "Program in processor has changed causing offline state. Do you want to upload?" RSLogix500 V8.10 Micrologix 1400 Customer wants to add...
2,263