Weight Control using Vibrofeeder
raul_vaze
Feb 2008
mumbai
87
Dear All ,
I am facing PID control for Discharge through a SILO onto a conveyor that has weight transmitter which gives me T/hr , each SILO has 5 cones and each cones has vibrating feeder to it and vibrating feeder has VFD for controlling the feeders . I am having difficulty controlling the Discharge through vibro feeder using PID control since it takes around 5 to 10 seconds depending on postion of vibrofeeder for the discharge to get reflected on the Belt Conveyor weight system. Any suggestion on how to go ahead with PID control
Proportional control is what it means it's proportional to the error
Most PID applications only use PI but in your case you may need to implement the D component
PI doesn’t have the capability to predict the behaviour of the error. So it reacts normally once the set point is changed. The D component overcomes this problem by anticipating the future of the error. Its output depends on rate of change with respect to time, multiplied by derivative constant it gives a boost to the output thereby increasing system response.
However, having 5 feeds with PID control might be a major drawback as one might fight another, I suggest you need to somehow slug the preceding silo feeds or even make them sort of fixed or limit their output to a fixed proportion of the required flow/weight, then control the final one to make up the required rate. However not knowing the application, whether the feeds are reasonably constant or run out or other factors I think it's a matter of trial and error with different scenarios.
“Weight Control using Vibrofeeder”...
Strapping a vibrator to your fork or spoon so that most of your food falls on the floor?
Sorry, couldn’t resist... :oops:
Hello All, I have two bags of two different types of peanuts hanging on a load cell above two separate feeders. I am using Studio 5000 and would...
45
8,837
I did some searching on the site before posting this, and came across Bob O's thread from a year ago...
3,453
I'm just starting to learn about industrial automation processes, I want to know how a weight feeder unit works which consists of a load cell and...
1,066
Hello Folks, plc : micrologix 1500 The analog output from the loadcell is given to the plc. Using the SCP function I have scaled it into an...
761
Mechanical engineers ask me a question with which I have no experience. They asked me to select a servo motor 100kw for a cutting application...
2,467